    Wiring mobile home 200amp
    I have a new mobile home 200amp service and I have built a pedestal and am installing both a meter box and a service disconnect which is about 42" from the trailer. Every website I have found recommends 2/0THHN copperwire for the two hot leads and 1/0 copper wire for the neutral. Is this correct or do I need different sized wire?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Aug 9, 2013, 08:03 AM
    That's fine for 200 Amps.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Aug 10, 2013, 07:13 AM
    Since the service point will outside of the trailer, you cannot use THHN type conductors.

    THHN is listed for use in "Dry" locations only.

    THHW is listed for Wet areas, also THWN-2, XHHW and XHHW-2. All of these would have to be in conduit.

    Using a multi conductor cable listed for direct burial (Type USE) is also a better choice.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Aug 10, 2013, 09:05 AM
    One more thought, because you are putting in a main disconnect switch at the meter, you cannot use Table 310.15(B)(7) to select your service entrance conductors 200 amp - 2/0 cable.

    You must use a 4 wire connection from the disconnect switch to your service panelboard. Which means that you need to use Table 310.15(B)(16). A 200 Amp feed requires a 3/0 cable if both the switch and the panelboard are listed for 75 (C) {167(F)}. If they are not listed for that temp, then you have to use the 60 (C) column which means that you would need a 250 kcmil cable.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #5

    Aug 11, 2013, 03:25 PM
    I am guessing/assuming the wire was THHN/THWN, as that is what most Electrical Supply House carry.
    Insulation is Important.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Aug 11, 2013, 03:39 PM
    Since the service point will outside of the trailer, you cannot use THHN type conductors.

    THHN is listed for use in "Dry" locations only.

    THHW is listed for Wet areas, also THWN-2, XHHW and XHHW-2. All of these would have to be in conduit.
    I realize this is a very popular thing to correct on message boards, but these days it is a non-issue. Most people just say THHN as a matter of habit, and pretty much all THHN is also dual rated THWN these days.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Aug 11, 2013, 03:41 PM
    One more thought, because you are putting in a main disconnect switch at the meter, you cannot use Table 310.15(B)(7) to select your service entrance conductors 200 amp - 2/0 cable.

    You must use a 4 wire connection from the disconnect switch to your service panelboard. Which means that you need to use Table 310.15(B)(16). A 200 Amp feed requires a 3/0 cable if both the switch and the panelboard are listed for 75 (C) {167(F)}. If they are not listed for that temp, then you have to use the 60 (C) column which means that you would need a 250 kcmil cable.
    Don, just because there is a switch outside does not mean these are not still the main power feeder conductors. NEC 2011 Table 310.15(B)(7) still applies.

    Remember, this table is for "Single-Phase Dwelling Services and Feeders"

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Mobile home wiring [ 2 Answers ]

I own a palm harbor 4 bedroom double wide. The front bedroom and the living room outside wall are without power. There is power coming out of the breaker box but stops before reaching there. Someone told me it is in the crossover. What do I look for to fix this problem?

Electric wiring diagram for mobile home [ 3 Answers ]

We need an electric wiring diagram for an 1989 or 1990 liberty mobile home

Mobile home service wiring. [ 2 Answers ]

What size and type wire do you use to connect electrical service to a mobile home

External Mobile Home wiring [ 2 Answers ]

I have 200 amp service poll with a 200 amp breaker box mounted on the poll, there are 3 wires from the meter to the box. One ground and 2 120 amp. No neutral wire. The poll has a ground wire in the ground beside it that the ground wire in the box is connect4ed to. I want run a line from bottom of...

Wiring a mobile home [ 4 Answers ]

I'm running the service for my trailer and I need some help with it. I have a 200 amp panel in the home and a 200 amp panel on the pole. But the panel on the pole only has one set of lugs on the top of the main breaker. Do I need lugs on the bottom of the panel to put the wire in from the trailer...