Ask Experts Questions for FREE Help !
Ask
    BillSartin's Avatar
    BillSartin Posts: 1, Reputation: 1
    New Member
     
    #1

    Jul 27, 2013, 03:36 PM
    Residential electrical service
    What size aluminum conductors needed for a 200 amp, 240 volt single phase, residential service that is in PVC conduit and 400 feet long?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jul 27, 2013, 05:05 PM
    Based on the information given, you would need 1000 kcmil conductors to keep the voltage drop below 3% and provide 200 amps at the main service panel.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #3

    Jul 27, 2013, 05:17 PM
    Based on the information given, you would need 1000 kcmil conductors to keep the voltage drop below 3% and provide 200 amps at the main service panel.
    Don, what are you basing this on? This is a bit absurd.

    A) We don't really use the 3% number for services
    B) We don't use the old 310.16 for residential single phase services
    C) We don't use the full amperage when figuring voltage drop


    Typically 250' is about the limit for "standard" service wire sizing. From there we go up in size until primary is the best bet.
    I'd go with 250mcm AL up to about 350' or so. Then up another size to about 400' or a little more.

    Best bet is to contact your local utility. They are usually the ones who will size this cable and tell you what to use.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    Jul 27, 2013, 09:56 PM
    Question for you Stan.

    How do you pull 3 wires that size and 400' long through conduit. I couldn't get that much wire off my truck.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Jul 28, 2013, 05:10 AM
    Stan,

    I used the Southwire voltage drop calculator. The options I used were:

    Single phase - Aluminum Cable - 240 V - Conduit and a working 200 Amps at the end of the cable.

    I know it is absurd, but that was what the OP asked for, 200 amp. Also, that is the site that TK told me to use.

    Don
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #6

    Jul 28, 2013, 06:25 AM
    How do you pull 3 wires that size and 400' long through conduit. I couldn't get that much wire off my truck.
    It's not fun, I tell you that. :/
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Jul 28, 2013, 06:26 AM
    I know it is absurd, but that was what the OP asked for, 200 amp. Also, that is the site that TK told me to use.
    Well, we normally don't use the full 200A number, 160 would be the highest I would ever use.
    Also, like I said, we use the other table for figuring single phase residential services, so the standard VD chart does not apply.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #8

    Jul 28, 2013, 11:36 AM
    Stan,

    The way I interpreted the original post, the requester was asking for a main service of 200 amps from a distance of 400' to the nearest connection point with the Power company. There was no mention suggestion that the OP wanted to take an 80% to the amperage.

    Also, the OP wanted Aluminum and was going underground and in conduit.

    I applied the Voltage Drop suggested / recommended percentages because of the sheer distance. Given that there is no way a 4/0 conductor would ever be able to deliver that working load that distance.

    A 250 kcmil Aluminum conductor will only deliver 200 amps across 182'. At 160 amps, the calculator I use would carry the 160 Amps half way.

    Please educate me if I am not doing this correctly.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Residential Service Cable Type [ 11 Answers ]

Once again, a res. Question by a comm. Electrician. I have a new project relocating a meter service. The new meter will be about 25 feet from the 200A panelbox location instead of back to back. I'll wire in a 200A 2 pole breaker at the meter location as per 10 foot tap rule, and run new cable to...

Safer residential service. [ 3 Answers ]

Which is safer L1-110 L2-110 With center tap to ground Or L1-220 L2 gounded Thanks

Residential cleaning service [ 3 Answers ]

My name is Mari. I recently started a cleaning company. I have already cleaned serveral homes but I am having a hard time as to what I am suppose to charge. I do not have much experience in this field but thought it would be a good flexible job while I am in school. I have tried to get advice...

150 Amp residential service [ 1 Answers ]

What size wire is needed for a 150 amp residential service?


View more questions Search