Ask Experts Questions for FREE Help !
Ask
    KWoodall's Avatar
    KWoodall Posts: 1, Reputation: 1
    New Member
     
    #1

    Jul 4, 2013, 02:08 AM
    How many amps in a garage? And Flickering lights
    I have two questions that hopefully someone more experienced than me can answer.

    Background: I am doing a claymation in a garage and need to set up a lighting system that requires (a.) lots of wattage and (b.) constant voltage so lighting stays extremely consistent [doesn't get dim or flicker despite other people using outlets].

    The garage is connected to about 20 other garages in an apartment complex, so it is not a typical house hold garage.


    Question 1: (A.) There is one outlet on the garage ceiling. How many amps would you assume is connected to this outlet (20? 50? 100?) It may be impossible to know but perhaps there is a standard amount of amps that apartment garages need to have. I figure it would have to be more than 20 because if 4 garages are opened at the same time, the breaker would trip.

    (B.) How many watts could I draw from this one outlet?

    (C.) How can I find out how many amps are in the garage? Where would the circuit breaker be to find it?

    Question 2: The lights I have set up go dim periodically (perhaps when others open their garage). How do I maintain constant light? (Voltage stabilizer, online ups?) I'm not sure what those are, but what is my best option to make sure those lights are always a consistent brightness?

    Thanks!
    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #2

    Jul 4, 2013, 09:17 AM
    The first thing you have to do is find out where the breaker panel box is. This info you should be able to get from the super or maintenance crew.

    Once you have that info we should be able to help you.

    Chuck
    sinnadurai's Avatar
    sinnadurai Posts: 127, Reputation: 2
    Junior Member
     
    #3

    Jul 4, 2013, 10:24 PM
    Provide the load(lights,sockets,equipment & wattage) connected in each garage and in which country(NEC,BS,VDE etc) is it located. If BS use ring circuit for outlets.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #4

    Jul 8, 2013, 02:39 PM
    Research a lighting system using LED lighting. We specify them for stages and small theaters... The amount of light is impressive and the power requirement is minimal...
    They may also be less effected by power issues.
    ebaines's Avatar
    ebaines Posts: 12,131, Reputation: 1307
    Expert
     
    #5

    Jul 9, 2013, 05:48 AM
    Most likely the circuit that the garage outlet is on is probbaly rated for about 20 amps total - meaning that's the level of amperage that would cause the circuit breaker to trip. If there are multiple garages on that one circuit, and given that when a garage door opener starts it causes a momentary surge on the line, I would estimate that you're probably good for about 10 amps of continuous current, or 1200 watts. You may be able to pull more current than that, but run the risk of blowing the circuit breaker if others on the same circuit also have a high demand for current (for examnple if multiople garage doors operate at the same time).

    The circuit breaker panel may be in the garage itself, or if these are dedicated garages for each apartment perhaps somewhere within the apartment itself. Do you know where the breaker panel is for your apartment?

    If flickering is an issue you should be abe to obtain a UPS that smooths out the momentary dips in voltage. These are quite common for use with IT equipment - servers and such - so take a look at TigerDirect.com.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Flickering lights? [ 3 Answers ]

Have a very brief & slight flickering of incandescent lights (on different circuits) every 45 seconds. Just started doing this during last week. Can't tell if the lights get brighter or dimmer - it happens so fast. No other electrical devices turned on that might cause flickering. Have an old...

Flickering Lights [ 2 Answers ]

All of the sudden... When we turn on our appliances downstairs, our lights in that area flicker. Why is this so? Should I be alarmed?? It has been doing this now for a couple of weeks. Thank You, Jenna Coy:eek:

Flickering Lights [ 2 Answers ]

Recently, we have experienced flickering lights at various spots throughout the house. As I'm typing this the lights just went off and back on and nothing else was on in the house. Our house is over 20 years old. Any idea where we should start investigating? It has never happened before.

Flickering lights [ 1 Answers ]

:mad: i have some lights that are flickering in the down stairs bath and hall and a small computer room what could be the problem? I think it could be a week braker, or a bad connection. What do you think. Thanks for any help.

Flickering lights [ 37 Answers ]

Bigg oops I thought I double posted the question some how and edited/lost the origonal Dangit will try to recompose it Issue of dimming lights, brightening of lights, constant flickering. All these would be a lot worse of a flicker when it is night time or windy out, but still quite often in...


View more questions Search