    100 Ft Electrical Wire Run?
    I need to run a 100 Ft Eletrical cable from the side of the house to my Shed.
    AndIt will need to be put underground. What kind and size wire do I need to buy? It will be used to run Battery Chargers, and small electrical tools.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Jun 5, 2013, 03:45 PM
    How much current do the battery chargers draw? Lithium batteries or golf cart-big difference. Radial Arm saw? You can run thhn/thwn in conduit or NMC direct bury but you need to figure total amperage and also adjust for voltage drop. #12 AWG is 20 AMP, #10 is 30 AMP, would not consider #14 AWG. I personally would do a home run #10 with a 20 AMP breaker into a couple of large junction boxes and then pigtail off #12 for outlets and lights. Almost impossible to get #10 into outlets or switches. Any #14 in the circuits would require a 15AMP breaker.
    catonsville's Avatar
    catonsville Posts: 894, Reputation: 91
    Senior Member
     
    #3

    Jun 5, 2013, 04:37 PM
    Quote Originally Posted by ma0641 View Post
    How much current do the battery chargers draw? Lithium batteries or golf cart-big difference. Radial Arm saw? You can run thhn/thwn in conduit or NMC direct bury but you need to figure total amperage and also adjust for voltage drop. #12 AWG is 20 AMP, #10 is 30 AMP, would not consider #14 AWG. I personally would do a home run #10 with a 20 AMP breaker into a couple of large junction boxes and then pigtail off #12 for outlets and lights. Almost impossible to get #10 into outlets or switches. Any #14 in the circuits would require a 15AMP breaker.
    Mainly I want to charge my 2 Deep Cycle Fishing Batteries using possibly 1 or 2 10 amp chargers in the summer and 2 trickle chargers in the winter time. Nothing heavy with the saw or drill equip.

    Not familiar with the thhn/thwn term. Also NMC. Was thinking of running #12 AWG inside of 1" white PVC pipe or whatever size pipe that would take 3 wire #12 and bury it about 3-4 inches in ground. The price of Copper may cause me to use a 100' extension cord and take up when not needed. ;) Less Labor Intensive too.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Jun 5, 2013, 05:19 PM
    THHN and THWN are stranded cable. NMC is Non Metallic Cable, also called Romex. Romex is not permitted in a conduit underground due to the moisture. "3 wire" assume you mean 2 plus a ground. 2 X 10 AMP chargers is 20 AMPS, max allowed on 12. You will have some voltage drop in 100 ft.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

What size wire do I need to run for a 100 amp garage panel [ 1 Answers ]

I have what looks like #2 wire. I want to know if it will handel 100amp service to my garage. The wire is copper braided counting outside sheating it's around a 1/4" in dia. I can't make out the number, maybe it's an 8. It did have 60amp breaker hooked up to it. I had a not electrical garage fire...

Electrical Sub Panel can I run a reduced neutral wire for 100 amp? [ 1 Answers ]

What size wire do I need to run a 100 amp sub-panel, I have #2 Aluminum 2-2-4 # 4 is the neutral

Wire UF wire to run to new 100 amp service panel? [ 10 Answers ]

My house has a 200 amp service. I have a new 30x40 building in back. I have a 100amp Square D load center for the building. I want to run a line from the house to power the building. Big items include, air comp 30 amps, welder 50 amps, other raidial arm saw, ban saw pipe saw 15-20 amps? It is...

Electrical sub panels 100 amp wire size [ 4 Answers ]

I want to put a 100 amp sub panel in my new attached garage. What size wire do I need for a approximate 65 ft run? Also, since the whole house is finished, I will have to come outside and run a conduit along the outside of the house to the garage. What size concuit do I need? Finally, what size...

Trying to run 2 100 amp subpanels -what size wire? [ 3 Answers ]

Ok, I am new to the site, but I have looked and looked and not found the answer to my specific questions. Many questions are similar but do not have the same specific circumstances and I have asked many people including electricians and I get different answers from everyone I ask so I am seeking...


View more questions Search