    Broken power line under ground
    Can I repair 3 #2 Aluminum wires going from the main breaker box (200 amp) feeding a 100 amp sub panel 50 feet away in a garage shop. We accidentally broke all 3 lines while digging up a tree. Can it be patched and re buried?
    It was not as deep as it should be.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    May 22, 2013, 07:45 PM
    You would need to cut back well into good wire. Do not splice it right where it broke. The cable is most likely stressed and contaminated within a couple of feet of the break.

    You'll obviously need six direct bury splices and heat shrinks, and enough wire to make up the difference.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    May 23, 2013, 05:57 AM
    If the Problem is close to one end, Maybe pull new wires on the short end and have 1 set of connectors.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    May 23, 2013, 08:05 AM
    If this is a direct feed from your main panelboard to a downstream panelboard, you MUST have a four wire feed!

    Also, within the downstream panelboard, Ground and Neutral must be isolated from each other.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    May 23, 2013, 01:23 PM
    If this is a direct feed from your main panelboard to a downstream panelboard, you MUST have a four wire feed!
    An older feed to a detached structure could very well be 3-wire and be perfectly legal. In those cases the grounds and neutral are bonded just as they are in a main panel.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    May 23, 2013, 02:38 PM
    I agree, but if the cable is severed as described above, and replaced. Wouldn't need to be replaced with a new 4 wire cable?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    May 23, 2013, 03:24 PM
    IMO no. It is just a repair.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Burnham Series 2 Gas Boiler is not receiving elec power , but main line has power up [ 0 Answers ]

Burnham Series 2 Gas Boiler is not receiving elec power , but main line has power up to the unit

Electrical partial-power-loss power to the outlet on one side and the ground [ 2 Answers ]

I have partial-power-loss as a result of a heater and christmas tree plugged in the same line in my home. The problem I 'm having is that each outlet that was affected still has 115V on ether side and ground , is this the result of a hot attaching itself to ground somewhere in my wall? And how...

Broken outlet. Hot and ground give power [ 4 Answers ]

Hi all. A month or so back I replaced an outlet in the kitchen with a GCFI outlet. This outlet apparently is the only thing on the circuit. Through this process I visually traced the wire through the basement and it seems to go from the outlet, down the wall, and into the breaker, no junction...

Broken Line [ 1 Answers ]

Hello All, I have a waste line in a downstairs bathroom that has collapsed under the ground. The only thing connected to this line is a toilet and small sink. I was wondering if I can cut the cast iron drain under the toilet in the crawl space and run a PVC elbow and 4" pipe from this...


View more questions Search