Ask Experts Questions for FREE Help !
Ask
    Reggie3260's Avatar
    Reggie3260 Posts: 2, Reputation: 1
    New Member
     
    #1

    Mar 7, 2013, 11:26 AM
    New bathroom installation with GFCI's & exhaust fan
    I'm running a new 20 amp. Line into our bathroom. I plan on using 12-2 cable. From the panel box I would like to put 2 GFCI receptacles (which will always be hot) and at the end of the run have a dedicated switch which will control an exhaust fan only (no light). My questions are:
    How would you recommend wiring the 2 GFCI receptacles (both single-location protection or should I wire the one nearest the panel for multiple-location protection? Also, am I correct that for the fan wall switch, all I need is a 20 amp. Single pole switch, and for the panel box, a 20 amp single pole breaker. Thanks for you advice.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Mar 7, 2013, 12:15 PM
    Reggie:
    I would always prefer using multiple GFCI's and keeping the GFCI receptacles separate and dedicated. I hate going to the basement to reset the bathroom. Also long conductors on the load side of a GFCI can cause nuisance tripping.

    If you are not concerned with doing this in accordance with the electrical code then putting the fan on circuit is fine...
    Otherwise If you do want to be compliant with the code and you're applying for a permit, the fan can be connected to the GFCI circuit but only if it is dedicated to that one bathroom. This means you will need a second circuit for the other bathroom. You can wire all bathroom GFCI's to one circuit but then you cannot connect other outlets...
    The code section is 2011 NEC 210.11(C)(3).

    ... and yes, a 20 ampere switch for the fan and a 20 ampere single pole circuit breaker with 12-2 NM is correct...
    Reggie3260's Avatar
    Reggie3260 Posts: 2, Reputation: 1
    New Member
     
    #3

    Mar 7, 2013, 01:47 PM
    Thanks so much for your quick response. Just so I'm clear. This is a second line I'm running to one bathroom. All other lights and plugs are on a separate line in this room. I also want to be sure I understand all of what you wrote: When you say you prefer using multiple GFCI's and keeping the GFCI receptacles separate and dedicated do you mean having each of them wired for single-protection? In my case both GFCI's would be wired that way? Second, since this line will be dedicated to this one bathroom and will only have those 2 outlets on that line, will connecting the and switch at the end of the line still be in accordance with the electrical code? Hope that makes sense??
    Thanks for your help and patience.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathroom Exhaust Fan Installation [ 5 Answers ]

I'm planning on installing an exhaust fan in my bathroom and I have a question about venting the air out of the house. I have read that normally you would vent the exhaust up and out the roof or sideways out the side of the house or soffit. Due to the location of the bathroom and set-up of the...

How do wire up a bathroom fan through a GFCI plug to a fan timer switch? [ 1 Answers ]

I am installing a Broan model# QTRE070C ceiling fan in my bathroom. I'd like to wire the fan through the GFCI plug to fan timer switch. The fan isn't going to be directly over the tub/shower enclosure but in the center of the bathroom ceiling. If it's not directly over the tub/shower will I still...

Bathroom exhaust fan [ 5 Answers ]

I just replaced the bathroom exhaust fan motor assembly which is the fan motor, squirrel cage, and mounting plate. I did this because the fan is about 25 years old. The bathroom is only 36 square feet with 8 foot ceiling and the new fan motor is rated at 100 cfm. The thing is that the fan does not...

Exhaust fan in bathroom [ 1 Answers ]

I am wiring a new bath and would like to know if code requires an Exhaust fan in bathroom.

Installation of a Bathroom exhaust fan [ 6 Answers ]

My source of power is originating from a light fixture and then goes to a switch. I've pulled a cable from the switch box to a bathroom exhaust fan and wanted to find out how to go about wiring it up. What would normally be a neutral wire (white wire) in this case ends up being the live wire...