    New GFI Circuit Breaker trips
    I just installed a GFI circuit from my breaker box and am faulting. I'm confident that I installed the breaker correctly with the breaker pigtail going to the power return bus and the black and white wires going to the correct terminals. If I operate the breaker without the earth grd connected it works properly but soon and earth is tied in it faults. I do have a GFI reset outlet as my first outlet of the string and this too is connected to the correct set of contacts on the outlet as are the other outlets in the string. I suspect one of two things is the problem.

    1) I noticed that some of the outlets I bought said self grounding and I'm assuming this may not be allowed.

    2) I did not series all of the outlets. I.E. In the box of my first outlet after the resetting outlet I feed the outlet in that box and two others. I'm thinking that maybe I should go to the outlet in the box and then to the next and then back to the third. I feel this is less likely but still it may be an issue.

    Please assist.
    nmwirez's Avatar
    nmwirez Posts: 453, Reputation: 20
    Full Member
     
    #2

    Mar 26, 2007, 04:56 PM
    Quote Originally Posted by HJSmith
    I just installed a GFI circuit from my breaker box and am faulting. I'm confident that I installed the breaker correctly with the breaker pigtail going to the power return bus and the black and white wires going to the correct terminals. If I operate the breaker without the earth grd connected it works properly but soon and earth is tied in it faults. I do have a GFI reset outlet as my first outlet of the string and this too is connected to the correct set of contacts on the outlet as are the other outlets in the string. I suspect one of two things is the problem.

    1) I noticed that some of the outlets I bought said self grounding and I'm assuming this may not be allowed.

    2) I did not series all of the outlets. I.E. In the box of my first outlet after the resetting outlet I feed the outlet in that box and two others. I'm thinking that maybe I should go to the outlet in the box and then to the next and then back to the third. I feel this is less likely but still it may be an issue.

    Please assist.
    The downstream circuit ground connections are in error if the Panelboard GFCI breaker trips when the white pigtail is connected to the ground terminal bus in the main disconnect panel. From what I gather this main GFCI is feeding into a receptacle GFCI and that is not needed. There may also be a shared neutral that does not allow having a main GFCI connection. Check that out once you have removed the wasted GFCI receptacle. Nm
    nmwirez's Avatar
    nmwirez Posts: 453, Reputation: 20
    Full Member
     
    #3

    Mar 26, 2007, 04:59 PM
    Quote Originally Posted by HJSmith
    I just installed a GFI circuit from my breaker box and am faulting. I'm confident that I installed the breaker correctly with the breaker pigtail going to the power return bus and the black and white wires going to the correct terminals. If I operate the breaker without the earth grd connected it works properly but soon and earth is tied in it faults. I do have a GFI reset outlet as my first outlet of the string and this too is connected to the correct set of contacts on the outlet as are the other outlets in the string. I suspect one of two things is the problem.

    1) I noticed that some of the outlets I bought said self grounding and I'm assuming this may not be allowed.

    2) I did not series all of the outlets. I.E. In the box of my first outlet after the resetting outlet I feed the outlet in that box and two others. I'm thinking that maybe I should go to the outlet in the box and then to the next and then back to the third. I feel this is less likely but still it may be an issue.

    Please assist.
    Did you mean 'self grounding' receptacles. If so those are commercial grade that are used with metal box and emt. Still need to ground to the green screw if residential and you are not in Chicago. Nm

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Lamp, trips, circuit breaker [ 3 Answers ]

My dog knocked over my lamp and tripped the circuit breaker, when I reset the circuit breaker it trips again. What could be the problem?

Replacing a circuit breaker with a GFI breaker- q on neutrals [ 1 Answers ]

In process on installing withquestion on neutral wires. Do you take the neutrals out of the in the main panel neutral and put them in into the breaker where its labelled "load neutral terminal" and only have the neutral "pig tail" to the panel neutral bar? Thanks!

Circuit breaker trips constantly [ 2 Answers ]

After eight years in the house without any problems now the oven circuit breaker keeps tripping as soon as the oven is above about 250 C. I turn off everything else that might be on this circuit and still the problem exists. Help!