Ask Experts Questions for FREE Help !
Ask
    emanuel9681's Avatar
    emanuel9681 Posts: 1, Reputation: 1
    New Member
     
    #1

    Feb 19, 2013, 11:29 PM
    how to wire
    I recently purchased a Ace brand programmable thermostat and some of the letters aren't on the new thermostat that are on the old one. Could any one help me!!

    Old: R = R
    G= G
    O= O
    Y = Y
    W2= B
    E= PURPLE WIRE
    L = WHITE WIRE


    New= A
    RH (jumper to RC)
    W2
    RC
    G
    Y
    W1
    O
    B
    C
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Feb 19, 2013, 11:56 PM
    C Black 24 Vac Common From one side of the 24Vac transformer (Think of this as 24Vac neutral
    R or V Red 24 Vac Power to be switched From other side of the 24Vac transformer (Think of this as 24Vac L1)
    Rh or 4 Red 24 Vac Heat call switch power Same as R, but dedicated to the Heat call switch
    Rc Red 24 Vac Cooling call switch power Same as R, but dedicated to the cooling call switch
    G Green Fan Fan switch on thermostat - is connected to R when Fan /Auto switch is in the fan position
    W White Heating call Is connected to R or Rh when themostat calls for heat. (Might be jumpered to Y on a heat pump. On others might be second stage heating
    [B]Y Yellow Cooling call Is connected to R or Rc when themostat calls for cooling. Also Cooling or 1st stage heating on a heat pump
    Most often connected to G when Fan switch is set to auto
    New signals - for heat pumps and staged systems[/B


    Y2 Blue or Orange 2nd stage Cooling
    W2 Varies Second Stage Heating First stage Auxiliary heating on a heat Pump
    E Varies,
    blue, pink,
    gray, tan Emergency heat relay on a heat pump. Active all the time when selected, usually not used. Disable the heat pump and turn on first stage Aux heating
    O Varies,
    Orange Reversing valve Energize to cool (Changes from heat to cool on heat pumps)

    B Varies,
    blue, black
    brown, orange Sometimes common side of transformer. Needed on some electronic thermostats or if you have indicator lamps
    OR
    Reversing valve (energize to heat) above. York and Trane sometimes use (B) as common. Might be heating changeover or on older stuff common of transformer.

    X Varies SEE NOTES BELOW Might be common but sometimes emergency heat relay
    X2 Varies Second stage heating or indicator lights on some thermostats Might be emergency heat relay
    T Varies,
    Tan or Gray Outdoor anticipator reset Used on GE/Trane/American Standard and some Carrier Products.
    L Varies Service Light

    Without model numbers this is as good as it is going to get.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Low voltage wire to heating element gets hot and melts the wire and burns wire into. [ 4 Answers ]

Where low voltage wire from sequencer plugs into heating element gets hot and melts the wire. What causes this? I changed the wire out, but it does it again.

Explain which wire is ground wire when you have 2 black wires and 1 white wire [ 5 Answers ]

Explain which wire is ground when you have 2 black wires and 1 white wire

Is hot wire is not a neutral wire or vice versa in single phase two wire AC source? [ 1 Answers ]

I am a little bit confused why in AC single phase 2 wire source is merely classified the 1 wire as hot and other wire as neutral. The hot wire travels the current from the source to the load and going back the current to the source through the neutral wire. I know that in AC circuit, the signal or...

Black wire red wire and white wire spliced to 10/3 on a 220 circuit [ 25 Answers ]

I have installed a disconnect between my dryer receptable and a tanning bed. I want to splice the 10/3 box wire to the existing 220 wiring at the dryer. Dryer= red, black, white and bare ground wires 10/3 wire= black, white, and bare ground How do I splice these to allow the disconnect box to...


View more questions Search