    Neutral Bus
    I'm installing new outlets in my garage with each having their own breaker. My issue is that my neutral bus bar is full (except 1 slot). Can I combine all the neutrals together and utilize the 1 remainig neutral slot? i.e. twist the 4 neutrals together and use a single neutral to the bus?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Feb 13, 2013, 11:11 AM
    You can buy buss extensions at HD or Lowe's.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Feb 13, 2013, 11:53 AM
    It is a NEC code violation to have more than one Neutral conductor in one hole!

    As ma0641 stated above. You can purchase Neutral bar extensions just about any hardware store.

    A word of safety, if you don't know what you are doing, Please hire an electrician, It is much cheaper than a hospital stay or a funeral!
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Feb 13, 2013, 01:34 PM
    Neutral bars are pretty rare to add on. It is a ground bar that is usually added on. You cannot put neutrals on a bar that is screwed to the back of the panel.

    If this is a main panel you can either double up on grounds of the same size, or add on a ground bar and move some grounds there.
    You cannot double up on neutrals though.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Feb 13, 2013, 02:46 PM
    Stan

    I stand corrected, thank you. I did searches at Lowe's and Home Depot websites.

    I found 1 (one) "Neutral Bus Bar extension kit". It is made by Schneider for a specific panel board. It had an insulating sheet, two plastic stand offs and the bar itself.

    So, what I have been seeing must be Ground bus bar extensions incorrectly used as Neutral bar extensions. I checked the time bomb I have for a panelboard and sure enough there are 2 such extensions.

    Tic -Tic! I better find some money and swap that panel out unfortunately, Social Security doesn't overpay us.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Ground vs neutral bus bars [ 4 Answers ]

I have a breaker panel (not a main panel with disconnect) which has two bus bars on each side, mounted on plastic insulating brackets, and which are connected together via a metal strap. The original electrician had connected the ground wires to one, the neutral wires to the other withouth...

No neutral bus in FP electric panel, what can I do? [ 4 Answers ]

I do know I need to upgrade the box but I need to install my electric dryer immediately for use. I have the breaker ready to install but have come across the problem of I see no neutral bus bar for the neutral wire. What can I do or can I install a bar on my own?

Can I add another neutral bus-bar to aservice panel? [ 1 Answers ]

I have more circuits that I can add onto my service panel but have run out of neutral slots on the bus-bar what can I do?

Neutral/Ground bus bar? [ 6 Answers ]

I am installing a sub panel in my basement to run some extra circuits for a bathroom, spare room etc. I am putting a 60 amp fuse in the main service panel, running a 6-3 wire with ground and back feeding the new sub panel. The new panel does not come with a ground bus bar, and suggests using...

What happen if you connect some grounds and neutral to the neutral bus bar and the do [ 1 Answers ]

The same conect some grounds and neutrals to the ground bus bar just using whichever bus bar is closest to the breaker so the wires don't have to travel all around the breaker box is that OK and safe to connect wires like that thank you


View more questions Search