    Feb 11, 2013, 04:26 PM
    Furnace with double breaker
    I'm putting in a Payne electric furance only, No air The furnace has 2 220 breakers, inside When I run my wire from The main breaker box to the unit, Do I put the wire on each side of the breakerand jumper in the middle or do I run the wire to one of the breaker. Thanks
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Feb 11, 2013, 05:32 PM
    On a 240 volt system there are 2 conductors and a ground. Using the appropriate gauge wire, one wire goes to each breaker and terminal on the heater. Ground goes from panel ground to ground terminal. There are no "jumpers ".PS 220 does not exist today in the US. Do not attempt to install a 240 circuit yourself if you don't know what you are doing. 240 will kill you!!
    bobclay65's Avatar
    bobclay65 Posts: 2, Reputation: 1
    New Member
     
    #3

    Feb 11, 2013, 05:35 PM
    Quote Originally Posted by ma0641 View Post
    On a 240 volt system there are 2 conductors and a ground. Using the appropriate guage wire, one wire goes to each breaker and terminal on the heater. Ground goes from panel ground to ground terminal. There are no "jumpers ".PS 220 does not exist today in the US. Do not attempt to install a 240 circuit yourself if you don't know what you are doing. 240 will kill you!!!
    OK thanks
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Feb 12, 2013, 07:01 AM
    Quote Originally Posted by bobclay65 View Post
    ok thanks
    If my answer was helpful please check "helpful ". Thanks
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #5

    Feb 13, 2013, 09:14 PM
    Quote Originally Posted by ma0641 View Post
    On a 240 volt system there are 2 conductors and a ground. Using the appropriate guage wire, one wire goes to each breaker and terminal on the heater. Ground goes from panel ground to ground terminal. There are no "jumpers ".PS 220 does not exist today in the US. Do not attempt to install a 240 circuit yourself if you don't know what you are doing. 240 will kill you!!!
    Ma, on some (Rheem, Rudd, & Weather King that I kow of) electric furnaces with a pair of double pole breakers you can run a common feed & install a jumper between the two internal breakers. The jumper kit is available from Rheem. It's the same principal as a breaker panel. The breakers are protecting what's downstream of them.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #6

    Feb 13, 2013, 09:21 PM
    Quote Originally Posted by Grady White View Post
    Ma, on some (Rheem, Rudd, & Weather King that I kow of) electric furnaces with a pair of double pole breakers you can run a common feed & install a jumper between the two internal breakers. The jumper kit is available from Rheem. It's the same principal as a breaker panel. The breakers are protecting what's downstream of them.
    I reread the post and did note "pair of 220" my bad. So in essence one breaker set protects the other? I am so used to straight 240 inHVAC and not paired.
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #7

    Feb 14, 2013, 05:39 PM
    Ma,
    No. The breakers (usually a 30 & a 60) each protect part of the load. For example: the 30 might be tied to the control system, fan, & 5kw of heat while the 60 is often tied to an additional 10kw.
    In an application such as this & with the use of the jumper, the electrician could run a single line capable of carrying the full load instead of having to run two lines.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Is 60 amp breaker the same as a double 30 [ 2 Answers ]

Is a 60 amp breaker the same a double pull 30 amp

Double pole breaker [ 3 Answers ]

Have a breaker it has two breakers 15amp each 30total. Both poles are ganged together so both trip together. Have loss power in six outlets. The others are okay. The breaker is reset. But still missing power in Part of the circuit. Should I replace the two pole breakers, since part Of the...

Double Double Breaker [ 10 Answers ]

I have a Square D breaker 150 amp panel box in my home. I wanted to put in a double breaker (20 - 20) but they don't make one for my particular box (it doesn't push in far enough to put the cover on). The guy at the store suggested I file out some of the matterial on the breaker so it pushes in all...

How do I determine breaker amps on a 240v double breaker? [ 7 Answers ]

Hi, I have a new elec. Cooktop that needs 240V, 40 amps. Each pole of the double pole breaker for my cooktop circuit Says 30amps. So can this 240v circuit support 60 amps, or just 30? Thanks!

Double breaker? [ 3 Answers ]

Hi, I have recently put in a new 200 amp. Service and had to install a large J-box to extend the wiring to the new location, (not very far). My problem is that I have a new 2-pole 40 amp. Breaker for the "A/C", and a 15 amp. Breaker for the "furnace". My confussion is that either of these breakers...


View more questions Search