    100 amp service installation
    Can I install a 100 amp service in a laundry room that is 5 ft 6 in by 4ft
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Feb 6, 2013, 02:04 PM
    If the voltage is 240V or less, then yes you can. You need to maintain 36 inches of clear space directly in front of the panel with at least 30 inches clear width...
    You can not install the panel directly above or below a domestic water line. Additionally, I would recommend keeping your distance from all water just for safety sake...

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Service entrance cable size for 100 amp and 200 amp service. [ 16 Answers ]

I would like to know what size aluminum sec I would need for 100 or 200 amp service

Overhead from a 100 amp service panel to a 100 amp subpanel in a garage. [ 6 Answers ]

An Electrician friend said I could use #4 copper for the (2)120 volt legs and a conventional Suspension wire as the nuetral. The overhead span is about 35 feet and the overall run From panel to panel is about 70 feet.The supply outlet said to use #2 copper. Also, what type wire for sunlight...

100 amp main, 100 amp service wire, 200 amp sub panel? [ 2 Answers ]

I am moving my sub panel and upgrading to a 200 amp service, but in phases. The first phase is to move the panel due to some remodeling. I want to put a 200 amp panel in the laundry room with a 200 amp breaker. I have 100 amp feeder wire going to it (AL 2/2/2). Outside I have the meter can and...


View more questions Search