    100 Amp - service for garage//shop
    Hello,

    Hoping someone here can point me in the proper direction. - I've read through countless articles online as well as about a dozen threads here on this board.

    I specified the General Contractor run a 100 Amp service to my detached shop. - I just checked the installation and he has 3 wire #6 copper free running through the attic. - The run will be about 200 feet total. Most websites indicate he needs to be using #4 at a minimum, with some recommending #2 due to the length of the run. - Can anyone point me to the NEC code or page in the book that specifies exactly what is correct so I can show it to him when we meet ?

    Thanks so much in advance.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jan 18, 2013, 05:25 PM
    Just tell him you know for a fact that #6cu is not good for a 100A feeder. If he tells you it is then fire him and find an honest contractor.
    Maybe it was an honest mistake?
    Kyle_in_rure's Avatar
    Kyle_in_rure Posts: 341, Reputation: 10
    Full Member
     
    #3

    Jan 18, 2013, 07:12 PM
    Just out of curiosity, Is there a 100 amp breaker currently in the main panel feeding the service to your shop?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Jan 18, 2013, 07:34 PM
    My first question to the GC would be, where is the plan you submitted and the approved permit.

    From the git-go there are severe violations. For example, A feeder from the main service panelboard to another panelboard requires a four (4) conductor cable.

    Table 310.16 must be used for the base conductor size. Then, although not a requirement of the NEC, voltage drop should be calculated. For 100 amps, copper using insulation listed for 75 C, #3 AWG conductors are needed. However,for a 200' run you need to use #1 AWG conductors.

    There are a lot more codes that deal with the remote bldg so my suggestion is to have a licensed electrician look at your plan before your GC does anything.

    Also whoever you decide on to do the work, make sure they pull the electrical permit in their name.
    NewHomeOwner13's Avatar
    NewHomeOwner13 Posts: 4, Reputation: 1
    New Member
     
    #5

    Jan 21, 2013, 02:57 PM
    Don, Thanks for the reply. It's in an unincorporated area so there are no permits required.

    I looked at the 310.16 code page and it surely does look like #3 should be what he uses at a minimum, #2, or #1 even based on the voltage drop.

    I'll get on the contractor to get this fixed.

    Thanks !
    NewHomeOwner13's Avatar
    NewHomeOwner13 Posts: 4, Reputation: 1
    New Member
     
    #6

    Jan 21, 2013, 02:58 PM
    Kyle, I do not have the building put up yet, but yes, there will be a 100 amp main panel when it is done.
    NewHomeOwner13's Avatar
    NewHomeOwner13 Posts: 4, Reputation: 1
    New Member
     
    #7

    Jan 21, 2013, 02:59 PM
    Stan, I'm with you on that logic, but the GC is overseeing everything. We just got to get the electrician straightened out. :)

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Overhead from a 100 amp service panel to a 100 amp subpanel in a garage. [ 6 Answers ]

An Electrician friend said I could use #4 copper for the (2)120 volt legs and a conventional Suspension wire as the nuetral. The overhead span is about 35 feet and the overall run From panel to panel is about 70 feet.The supply outlet said to use #2 copper. Also, what type wire for sunlight...

How to wire for a 100 amp service to a garage from a 200amp service location [ 1 Answers ]

I have a 400 amp service that is attach to my house and I going to be putting in a garage about 200 hundred feet away from the main service panel, I would like to know what size wire to use for that length.

Service entrance cable (alum) size for a 100 amp service at 186 feet for a garage [ 1 Answers ]

The garage is 186' from the service at the house. I wanted to make sure the voltage drop would not cause a problem.

100 Amp garage service [ 5 Answers ]

How do I run a 100 amp service off a 200 amp service? The part I need to know is where to hook up the aux. service in the 200 amp panel.


View more questions Search