    Causes breaker tripping sauna heaters
    Have sauna - gfi breaker tripping when heater gets up to temp replaced with regular 30 amp 2 phase breaker the system works perfect. Suggestions problem??
    Kyle_in_rure's Avatar
    Kyle_in_rure Posts: 341, Reputation: 10
    Full Member
     
    #2

    Jan 17, 2013, 07:10 PM
    Was the gfi breaker you replaced also 30 amps?
    albert62's Avatar
    albert62 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jan 18, 2013, 09:03 AM
    Quote Originally Posted by Kyle_in_rure View Post
    was the gfi breaker you replaced also 30 amps?
    Kyle

    The panel had a 30 amp GFI breaker in it. I switched it to 40 amp GFI breaker yesterday which is called for on the 6000 watt heater. The electrician tested the load on wires to peak at 35 amps. Both tripped when heater reached temp setting. With a regular 30 amp 2 phase breaker the system works fine!!

    Mike
    Kyle_in_rure's Avatar
    Kyle_in_rure Posts: 341, Reputation: 10
    Full Member
     
    #4

    Jan 18, 2013, 09:58 AM
    GFIs are known to sometimes have nuisance tripping due to their sensitivity. As to whether you can leave the nonGFI breaker in there or not, I can't answer that because I am not an electrician. Hopefully someone can provide a better answer. The breaker does need to stay 30 amps, assuming the wire is 10 awg. Hope this helps.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #5

    Jan 18, 2013, 10:19 AM
    Mike,
    You first need to review what the manufacturer's requirements for what the "listed" circuit breaker size and type are... It's not just an electrical code requirement (I assume you are in the USA) but it's a liability issue.

    All saunas and hot tubs I've seen require GFI circuit breakers for power. If you replace this with a normal circuit breaker and someone gets hurt, it's your fault! If you have installed the sauna in accordance with the manufacturers installation instructions and have a problem, you need to contact the manufacturer for their solution or recommendation. The GFI breaker is a safety feature, not an option.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can I use a switch to share the 50 amp breaker with hot tub and sauna? [ 3 Answers ]

I am out of room on my electrical panel and my wife bought a steam sauna. I heard I can put a "switch" or "converter" on the 50 amp panel I use for my hot tub. When she wants to use the sauna it will shut off power to hot tub and supply power the sauna. Is this accurate?

A/C Breaker is tripping [ 2 Answers ]

I have an AC unit that I replaced the condenser fan in last year. This year during a storm the AC breaker on the inside of my house went bad. I replaced it and the AC worked fine for a few day. Last night I noticed the breaker had tripped. I reset the breaker and it runs for about 15-20 min. and...

Breaker Tripping [ 4 Answers ]

Hello, I'll try to be as detailed as can be. I understand how electric circuits work but do not have a lot of experience with troubleshooting them. The problem is a tripping breaker whenever I turn on the associated ON/OFF switch. The switch connects to a lightbulb fixture and another wire...

Gfci breaker + outlet in same circuit.breaker tripping [ 4 Answers ]

I have a gfci breaker for a bathroom and there is an additional gfci outlet in the bathroom on the same circuit. The breaker was tripping intermittently over the past week and now will not re-engage. Should I suspect a faulty breaker or is it better to troubleshoot the circuit first? The...

Breaker keeps tripping [ 1 Answers ]

We have recently purchesed a Vits spa from some one. When we did we replaced the heat element . It has worked well for the last 6 weeks but now it it tripping the breaker on the heater. Any suggestions.


View more questions Search