    What wire size (copper) is needed for 30amps for 350 feet away from panel to subpane?
    I am 350 feet away from my breaker panel in the house to a shop I am planning on using. I need a 30amp 240 volt service for my wood working saws and lights. What size wire do I need to handle the voltage drop. Thanks Jim
    Kyle_in_rure's Avatar
    Kyle_in_rure Posts: 341, Reputation: 10
    Full Member
     
    #2

    Jan 14, 2013, 05:20 PM
    Normally a 30 amp load requires 10 awg wire, not sure at that distance though, you may want to go up to 8 awg wire to reduce voltage drop. Someone else will provide input.

    I assume you are going to run this to a subpanel in the shop. If this is the case, why not use 6 awg wire and make it a 50 or 60 amp subpanel? This would leave room for expansion in the future.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #3

    Jan 14, 2013, 05:56 PM
    For every 50' of run you need to up to the next heavier wire. I'd just go with #1and be done with it.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Jan 14, 2013, 06:27 PM
    For every 50' of run you need to up to the next heavier wire.
    Sorry ballen, this is just not true. It may have been an old wives tale back in the day, but we do things a little more accurately now.
    You need to do a calculation to be sure.

    With a load of 30A @ 240V I get #4cu
    With a load of 20A @ 120V I get #3cu.
    Both of these are realistic numbers for this installation.
    Ironically, the more things running the lower the voltage drop, assuming the load is pretty well balanced. Voltage drop @ 240V is dramatically less than @ 120V.

    Personally, I'd go with #4 and a 50A breaker. This is more than safe and reliable for such a feeder.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #5

    Jan 14, 2013, 08:28 PM
    Why copper? You will have a heart attack when you pay for that much copper and that distance. What would the local utility charge for a pole and drop?
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #6

    Jan 14, 2013, 08:40 PM
    Stan thanks for the info but can you show me how to do this calculation and why a 50 amp when the op says he only needs a 30? Xcbuilder, are you running 240 or 120, I'd do 240 for some shop equipment but I don't know exactly what you have planned.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Jan 15, 2013, 05:24 AM
    Stan thanks for the info but can you show me how to do this calculation and why a 50 amp when the op says he only needs a 30? Xcbuilder, are you running 240 or 120, I'd do 240 for some shop equipment but I don't know exactly what you have planned.
    I don't do the math, I use an online calculator. In the field I have several apps on my phone and iPad.

    I would go with a 50A feeder because even though he says he only needs 30A that is a long way to run if he needs more someday. IMO anything less than a 50A sub-feeder is silly.
    Also, I like to sometimes check what the drop will be at different amperages and at both 120v and 240v.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Jan 15, 2013, 06:24 AM
    Bal the most accurate formula recommend by IEEE is :

    Vd= 2*I*L*R/ft

    Which is what the on line calculators use. So much easier to use the on line calculators.

    While the poster requests copper wire, I would suggest #2 aluminum in a 4 wire URD direct burial cable. If soil conditions are rocky I would sleeve in 3 Inch PVC conduit for extra protection.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #9

    Jan 15, 2013, 07:05 PM
    Don't we need to know if he is going 120 or 240? The calculator I tried to use requires the voltage
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #10

    Jan 16, 2013, 02:35 AM
    Xcbbuilder states:

    I need a 30amp 240 volt service

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to find wire size for 60 amp panel 350 feet away [ 2 Answers ]

I'm building a shed and its 350 feet away from 200 amp service and I want to put in aluminum wire and I need to no what size to use

What size wire to a 200 amp panel 200 feet away [ 4 Answers ]

What size wire and how much for a 200amp box 200 feet away? I have a 200amp panel on a pole and want to run another box some 200 feet away to a man cave. It will house a fridge, lights, a window ac, and TV stereo. No heat as it will be wood burning stove. Gas oven and cooktop, one big 1200 sq ft...

Sub panel load size from main panel 200 amp to 100sub 350 ft [ 1 Answers ]

Wire conduit size fromm a main 200 amp panel to a 100 amp sub panel 350 ft away

Wire size for a 100 amp sub panel 200 feet away [ 8 Answers ]

I have a 200 amp main panel in my house and I just built a garage and am planning on putting a 100 amp sub panel in the garage. The garage is about 200 feet from my house and it has a 2 inch pvc stubbed out underground. I am wondering what size aluminum I would need to feed it, and if I can use a...

Subpane wire size [ 1 Answers ]

Another question regarding a large shop/barn I am wiring. The main service will be a 200 amp panel. Since the distance from the main service panel is so far to the other side of the barn, I thought I would put a subpanel in the middle of the barn (where the shop section will be). There are two...


View more questions Search