Good morning all -
Quick garage circuit question here. I am running a new circuit to a garage (only purpose being for garage door opener, 2 fluorescent lights, and 1 outlet -- as I believe that would be required). Planning on a 20amp circuit, using 12/2 underground feeder.
Because this is only 1 branch circuit, it is my understanding that the NEC would not require me to install a sub panel and extra ground rod at the garage... but would I need a disconnect switch in the garage?
Thanks in advance!
|
|
 |
Uber Member
|
|
Jan 13, 2013, 09:20 AM
|
|
Correct, a ground rod will not be needed for one 120 volt circuit, and one single pole switch at the point of entry into the garage can act as a service disconnect switch.
|
|
 |
Printers & Electronics Expert
|
|
Jan 13, 2013, 11:05 AM
|
|
How far is the garage from your main service panel board?
Also, if you bring electrical power into a remote building, you must put a light an entry light at the entry way to the building (not the garage doors).
FYI - if you are in a fairly cold area you might want to re-think fluorescent lights. They start poorly in cold temps.
|
|
 |
Junior Member
|
|
Jan 13, 2013, 03:24 PM
|
|
Garage is probably about 25' from the house -- any particular reason?
I figured the easiest buying method would be UF in a trench.
The garage does not have an entry way other than the garage doors. Also not my garage, fluorescent lights are already there. Just fixing how the garage is currently wired, which is 12/2 NM cable strung from the top of the house to the garage. Looks great, and very code compliant. (sarcasm)
|
|
 |
Printers & Electronics Expert
|
|
Jan 13, 2013, 03:44 PM
|
|
I was concerned about voltage drop issues. At 25 feet, there is nothing to worry about.
|
|
 |
Junior Member
|
|
Jan 13, 2013, 03:47 PM
|
|
Gotcha - wasn't trying to be snotty, just interested regarding what to consider.
Thanks!
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Replaced circuit breaker still no power to garage
[ 5 Answers ]
There was an overload many times on this specific breaker, and we replaced it and there is still no power to the garage. It was a double switch 20 amp circuit breaker/fuse that was replaced, and the main switch outside to the power was shut off before we replaced the breaker. There was a severe...
Garage opener and Bsmnt outlets in same circuit?
[ 7 Answers ]
Hello all:
I want to get started installing aprox 6 electric outlets in my basement but still have a doubt about it.
After making the study of which would be the best route/circuit to use, I've found I can only use one, from two going to the basement: circuit having the garage door (and light),...
Garage circuit issue
[ 3 Answers ]
Hi, I have a CKT for my garage lights and outlets(garage dr. opener), breaker seemed to have tripped , checked it , it is OK, checked voltage @ switches and outlets on CKT, and I have 80 VAC at first swicth on CKT, 120 VAC out of breaker. Question is what would cause this loss in voltage on such a...
Garage Door Circuit
[ 8 Answers ]
We are in the process of selling a house in Oregon and the inspector noticed that the garage door opener was plugged int the ceramic light fixture. The request that a outlet be installed for this purpose. Can we branch an outlet off the light or do we need to have a dedicated circuit for the...
View more questions
Search
|