    Aire flo furnace troubleshooting
    Aire-Flo AF90MPE075 - on a call for heat the combustion blower runs, pressure switch closes, his glows and gas valve opens for a split second. Sometimes the inrush of gas is not enough to even ignite and sometimes it is enough to ignite across the burner but then goes out immediately. Again, this all occurs in less than 1 second - not enough time to eben attempt to prove flame.
    After 5 or 6 trials the LED light flashes 3 times (pressure switch stuck open or closed). When a no call the switch is open, when combustion blower run it is closes - I even jumped it to make sure.
    When 24V put directly to the gas valve it stays open until power taken away.
    120V supplied to furnace. 25V from R to C. 120V from hot (black) to neutral (white) and ground.
    My thoughts: bad ignition cntrl board. Am I missing something? TY
    Grady White's Avatar
    Grady White Posts: 1,417, Reputation: 59
    Ultra Member
     
    #2

    Oct 17, 2012, 07:10 PM
    Check your vent system. Make sure it is clear with no sags. Sags in a horizontal run will trap water & cause exactly the symptoms you have.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

700 vs 750 millivolt thermostat for wall gas furnace saf-aire by stewart warner [ 5 Answers ]

All the new thermostats I have found that are "millivolt" say they are for 750 millivolt and the existing one I am trying to replace says it is 700. Can I install a 750 millivolt thermostat on this wall furnace? If not, please suggest where I can get a 700 MV thermostat.

I have an Aire-Flo gas furnace - model no. AF80MPA075B3A [ 1 Answers ]

I have an Aire-Flo gas furnace - model no. AF80MPA075B3A I rent - however I believe it was installed around 2003. For the last month - the furnace will start, the gas tries to ignite but after 2 seconds it will shut off. It tries to ignit 3 times - then if unseccessful the furnace shuts off. It...

Aire-Flo gas furnace periodically shuts down. [ 2 Answers ]

I have an Aire-Flo gas furnace - model no. AF80MPA075B3A I rent - however I believe it was installed around 2003. For the last month - the furnace will start, the gas tries to ignite but after 2 seconds it will shut off. It tries to ignit 3 times - then if unseccessful the furnace shuts off. It...

Aire-Flo Gas furnace Not Starting [ 1 Answers ]

I have an Aire-Flo Furnace ( Model AF90MPE075U3). Last winter it began malfunctioning. The local repair man said the inducer fan was bad and replaced it. It worked for a while and began acting up again. He then decided the intake air line was to small and not sloped properly. I added a second line...

Gas furnace not blowing hot air but blower is working fine. I have an Aire-flo AF80 [ 1 Answers ]

I have an Aire-flo model AF80 forced air furnace that is not putting out any heat. The blower is working fine. I have tried the circuit breaker and replacing the thermostat but neither seems to work. Anyone have any suggestions?


View more questions Search