Ask Experts Questions for FREE Help !
Ask
    steve101010101's Avatar
    steve101010101 Posts: 1, Reputation: 1
    New Member
     
    #1

    Oct 11, 2012, 07:58 PM
    New basement wiring issue
    Hi there.
    Am wiring my unfinished basement with new wire, outlets, lights, etc. Only thing that was in it was a 14/3 spare. Split that and sent one-half to two single pole switches and 6 can lights total (4 can & 2 can). Used 14/2 AWG romex on everything. Changed breaker to a 15 amp ARC fault interrupter breaker per local code). Very careful not to let wires touch, everything tight, etc. Issue is every time I try to turn on light to see if I did the job right it pops the breaker. Thanks in advance
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Oct 11, 2012, 08:55 PM
    We don't know how you wired the basement but you obviously have done something incorrectly, wires crossed, grounded or connected wrong. If you used switch loops make sure the hot goes to the switch and not the neutral. You discovered the beauty of a breaker though, not having.to replace a fuse. Not sure of using a split neutral on an AFCI, they do not work with a GFCI.
    Kyle_in_rure's Avatar
    Kyle_in_rure Posts: 341, Reputation: 10
    Full Member
     
    #3

    Oct 11, 2012, 08:56 PM
    Also double check you don't have the red and black touching anywhere (like on receptacle screws)
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    Oct 12, 2012, 04:48 AM
    Only thing that was in it was a 14/3 spare.
    Tell what that means, exactly.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #5

    Oct 12, 2012, 05:22 AM
    A single pole Arc Fault circuit breaker will not work using a shared neutral.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #6

    Oct 12, 2012, 01:19 PM
    OK,

    You are confusing the world here. The term, "14/3" describes a three conductor cable that also has a bare ground wire inside the cable sheath.

    This type of cable can easily be used in a multiwire circuit. I say this because it may be that the room was wired as part of a multwire circuit and you dismantled only half of the circuit.

    Is that possible?
    jefferson17's Avatar
    jefferson17 Posts: 17, Reputation: 2
    New Member
     
    #7

    Oct 18, 2012, 11:05 PM
    Even if local code allows it, you really should have the outlets and lighting on separate circuits. 15 amps for lighting and 20 amps for receptacles is pretty standard - each with a separate AFCI breaker. If ALL you are going to put on those few outlets are lamps, a stereo, etc then OK - 15 amps will do. But it may not be code-compliant.

    Those arc fault breakers are SUPER sensitive. Your wiring needs to be pretty much perfect, well tightened-down and capped off with wire nuts / tape etc. if you are mingling new wiring with older stuff then there can easily be something going on that is getting in your way. I'd start with just the outlets, with a dedicate home run and get that up and running. Then do the lights next.

    Good luck!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Wiring issue [ 3 Answers ]

I am attempting to wire a ceiling fan in place of a light fixture. There are two ceiling fixtures controlled by one switch. I wish to hard wire the fan so it works independent of the other switch controlled fixture. How do I accomplish this?

Basement floor level issue [ 1 Answers ]

Concrete basement floor at my house is not leveled. The high level is at the middle of the rooom and slope towards the wall. The high level at the middle of the house is about 2 inches higher than floor near the wall. Can you please suggest what are the options I have to level the basement floor?...

Wiring issue [ 1 Answers ]

Hi, I have a similar issue that you had. My eight wires match yours exactly. Did you ever find the proper pairs? Your help would be greatly appreciated. Thanks.

Basement drain issue [ 13 Answers ]

My home as a drainage system that consists of several pipes and tile that meet at a 4" pipe that exists out into a valley on my property about 100' feet from the house. The issue I am having is this same system is also hooked in to 4" drain in the basement and in the spring when we have ice...


View more questions Search