    Reason for 10-Foot Rule Between Meter and Breaker Panel
    While doing some work for me, an electrician looked at the lug-type breaker panel and advised me to change the panel to include a main breaker. However, the meter is located significantly over 10 feet away from the panel. Several web sites suggest that a main breaker is only appropriate if the meter is within 10 feet of the panel. Why is that so?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Oct 4, 2012, 10:21 AM
    The "10 foot Rule" for this application is not written down in the Code, anywheres.

    It comes from the Tap Rules, that does not apply here.

    The service entrance conductors that enter a building shall terminate at the " inside nearest the point of entrance of the service entrance conductors".

    Many, (not all) inspectors, allow up to 10 feet of these conductors to pass through a building to get to the Main Service Disconnecting Means, AKA Main Breaker.

    Consider this, these wires have NO short circuit protection, until they get to the Main Breaker.

    If someone were to drive a nail into these wires, they will burn until something melts clear.
    Missouri Bound's Avatar
    Missouri Bound Posts: 1,532, Reputation: 94
    Ultra Member
     
    #3

    Oct 4, 2012, 09:21 PM
    ... and that is the only answer required.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Looking for a 50 amp breaker compatible with a milbank meter breaker box. [ 1 Answers ]

Want to add a 3 or 4 wire 200 amp run from street meter breaker box (Milbank) to a electric stove.

Can I pull meter head to relocate breaker panel [ 4 Answers ]

I need to move my panel to the meter location (20 feet) as the main feed wire is on the inside of the house and runs about 20 feet. I'm told that this isn't up to code? I live in Pgh. Pa. Thanks for any advise, John

Back to back meter base and breaker panel [ 9 Answers ]

Hi, I want to mount meter base and breaker panel back to back, running the cable through the back of the meter into the back of the breaker panel. Breaker box will mount on a 2X4 exterior wall, and I would connect the two boxes with 1 1/2 nipple. Is there a problem with this idea? I'll be talking...

Ten foot rule-confused.. [ 3 Answers ]

I've read various posts concerning the 10 foot rule where a disconnect is needed at the meter if the load panel is more than 10 feet from the meter. This is of interest to me since I would like to relocate my load panel. Question #1-Am I interpreting this correctly? Question #2- If using a...

6 Foot Rule & Radiators [ 2 Answers ]

Is a wall with an iron steam radiator within 4 inches of the wall considered wall space when determining receptacle distance with the 6 foot rule? I have looked in article 210 of the NEC 2005 and have not been able to determine a definitive answer. Thank you.


View more questions Search