Ask Experts Questions for FREE Help !
Ask
    eric courtney's Avatar
    eric courtney Posts: 1, Reputation: 1
    New Member
     
    #1

    Sep 10, 2012, 07:26 AM
    Wiring multiple 220 single phase for welders
    We have a fabrication shop and I need to run 5 more single phase 230 plug ins for our welders. How do I go about this?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Sep 10, 2012, 08:13 AM
    Do you have the amperage capacity for this number of welders? You need to do a load determination vs. wire ampacity and if acceptable, add the additional outlets. Or, you may need a new service for the welders. We know nothing about your welders, Stick, TIG, MIG?? Get the info from the plates on the welders.
    shuntripper's Avatar
    shuntripper Posts: 180, Reputation: 8
    Junior Member
     
    #3

    Sep 16, 2012, 09:02 AM
    Standard plug that comes on many welders is Nema 6-50P, receptacle is 6-50R. As long as you have 8 unused CB spaces in a panel, they will each come from one two pole 50A CB. Your main will trip at this panel if you exceed it's amperage rating though.

    Do you have single phase or 3 phase power at the panel? If you have 3 phase do you know if you have a high leg in that panel? What is the main/disconnect amperage rating for that panel? Is the panel fed from a transformer?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

220 single phase wiring [ 2 Answers ]

I have a new 1 1/2 HP lawn irrigation pump. It was wired for 110 volts And runs to a 25amp breaker. It works fine unless the pump runs for More than 4 or 5 minutes. Then the breaker blows. The pump can run On 220 as well. I have a receptical in my garage that is 220 and has Two flat poles and a...

Converting 220 Single Phase Euro outlets to 110 volt two Phase Us ones? [ 1 Answers ]

I want to convert a euro single phase 220 volt outlet to a 110 outlet

Convert 240 volt 3 phase to 220 volt single phase [ 2 Answers ]

Hi I have a 3 phase 250 volt 30 amp socket .I want to know if I drop one leg and change the receptacle . Can I plug a 200/230 volt 48/42 amp miller welder in to it ? Do I just wire nut the extra wire or pull it out of the panel ? Thanks mike

208-220 single phase [ 1 Answers ]

Can I run a 220 single phase dc motor controller on 208 single phase ? Any help would be great.thank you Bob

Running 220 single phase from generator? [ 1 Answers ]

I recently bought a wood planer. The id plate on the motor tells me it is 3 hp wired 220 single phase. The planer plug has three prongs on it. I plan to use this in my shop. My shop is powered with a 7000 watt generator. My generator has 220v but it has a 4 prong plug. CAn I change the plug on...


View more questions Search