    how watts of load could be supplied by a 200amp 230v 3 phase connection
    We are making a pizzhut on a building taken on rent. They are supplying 200amp 230v 3phase connection. Our load requirement is around 165kw. Is this supply enough for our restaurant to run smoothely. Please give me a clear reply explaining how to calculate these all stuff. I know that W=A*V. But for 3 phase connection how it works?? I don't know.. please help me..
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Aug 26, 2012, 07:20 PM
    Quote Originally Posted by ajan View Post
    We are making a pizzhut on a building taken on rent. They are supplying 200amp 230v 3phase connection. Our load requirement is around 165kw. Is this supply enough for our restaurant to run smoothely. Please give me a clear reply explaining how to calculate these all stuff. I know that W=A*V. But for 3 phase connection how it works??? I dont know.. please help me..
    I'm sorry, but I will not do this for you, and you should not be concerned with this yet either. It's not my job and it is not yours either.

    Get a licensed competent electrician to bid this job and then he can and should do a load/service calculation for you.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #3

    Aug 27, 2012, 01:34 PM
    You really need to be talking to your designer and a licensed "Master" electrician to get these answers.

    You have give no useable information. For example, how many ovens are you planning for and what auxiliary equipment do they require? What are the lighting requirements for your restaurant both cooking and eating areas? What other equipment are you going to have? What appliances will be gas fired?

    These are all relevant questions and they fail to be even close to being all the questions that need to asked and answered.

    Certainaly, this site, which is a DYI residential wiring site is not equipped to do commercial planning for a restaurant.
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #4

    Aug 28, 2012, 04:03 AM
    If this is a Real Estate leasing question and you are negotiating terms and they are
    Offering you 200A, 230V, 3 phase and you know that your typical load requirement is
    165 kW... then no, this represents only about 40% of the power you require.
    165 kW translates to approx. 600 ampere, 230V, 3 phase service.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Powering single phase load with 3 phase generation [ 4 Answers ]

How to select a 3 phase generator for 75kva of single phase load calculated

Service for 3 phase 200amp [ 8 Answers ]

Can I use sweet brier for 3 phase 200amp service run from the pole to the meter? Jim

I have read that a circuit can drive a 7 ampere load.how mny watts?=7A load. [ 4 Answers ]

What appliances in our home work on 7A.) how to relate the ampere to watt conversion(eg:a bulb of 15 w need how many amp of current?

Receptacle wiring 230v single phase [ 17 Answers ]

I have a 2hp compressor which is labeled Volts 230/115; PH1. The compressor is not going to be used that often. I would like to plug the compressor into an outlet which was used for a clothes dryer at one time. The outlet has a 10/3 conductor connecting it to double breakers which are labeled...

How am I going to size my 3 phase X'mer with 1 phase load using current as reference [ 3 Answers ]

Hi, I'm Peping: I have 90 pieces of single phase loads with current of 2 Amperes. This will be loaded to a 3 phase transformer, Wye connected having a line to line voltage of 220 Volts. What will be the size of the transformer required for the mentioned loads? Many thanks, Peping