    100 amp subpanel - wire to use
    What wire should I use for a 100A subpanel to be located about 100 ft from house (200A) in a pole building. Is #3 copper (3 wires) and a #8 copper ground OK? Could I use 2-2-2-4 MHF?
    mike 165278's Avatar
    mike 165278 Posts: 168, Reputation: 7
    Junior Member
     
    #2

    Jul 30, 2012, 06:56 PM
    The #3 copper is good for 100 amps but at 100' you're pushing it. Better to go with a #2 or even #1 with a #6 ground. I'm not sure what a pole building is, but you'll have to drive a ground rod at the subpanel. Is it a steel building?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Overhead from a 100 amp service panel to a 100 amp subpanel in a garage. [ 6 Answers ]

An Electrician friend said I could use #4 copper for the (2)120 volt legs and a conventional Suspension wire as the nuetral. The overhead span is about 35 feet and the overall run From panel to panel is about 70 feet.The supply outlet said to use #2 copper. Also, what type wire for sunlight...

Three Wire Aerial Feed to 100 amp subpanel [ 3 Answers ]

I am hooking up a 100 amp subpanel with a 2/2/2 overhead wire. Is the overhead bare wire a neutral or a ground? Should I take the connector bar out that is pre-installed in the subpanel between the neutral and ground bars? Should I bond the panel with the bonding screw? (I am backfeeding the sub...

100 amp main, 100 amp service wire, 200 amp sub panel? [ 2 Answers ]

I am moving my sub panel and upgrading to a 200 amp service, but in phases. The first phase is to move the panel due to some remodeling. I want to put a 200 amp panel in the laundry room with a 200 amp breaker. I have 100 amp feeder wire going to it (AL 2/2/2). Outside I have the meter can and...

How many conductors to wire a 100 amp main breaker subpanel in detached garage. [ 3 Answers ]

How many conductors do you have to run to a main breaker subpanel which is located in a garage 100 ft away. Can you get away with 2 hots and a neutral If you pound a ground rod at the subpanel. I cannot find the answer in the code book.

Can I run a 50 amp subpanel if a 100 amp main if so what size wire [ 1 Answers ]

Can I run a 50 amp subpanel from a 100 amp main and if so what size wire


View more questions Search