    Circuit breakers fail but don
    I have a very strange problem with 3 different circuits failing but the circuit breakers are not tripping. The service to the house is 100 amps and there are 16 subcircuits each on their own 20amp square D breaker. My lights flicker on one circuit and within 10 minutes all 3 circuits (two are on the same center bar - #7 and #8, the 3rd is #3, not adjacent) go out but the breakers don't trip. The breakers are not tripped and there is no red indicator popped up. Turning the breakers off and then back on does NOT fix the problem. Waiting 20 minutes and the power is back on working all 3 circuits. These circuits will come back in 20 minutes whether I throw/reset the breaker. Makes no difference. The circuits will then work for about 3-5 days and then it happens again (3 time now). I feel the breakers and they all are cool (all 16 of them), no heat. I would think if it was just one circuit that I had a short in the circuit and after it cools it come back on, but they are all different circuits and there is no cross circuit wiring. This wiring was done new in about 1995 so it is all fairly new and they have run without a problem for the past 16 years. I'm stumped, hope you can help.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 30, 2012, 02:38 AM
    Could be a loose neutral connection in the utility feeder, meter, or panel. Could be a loose bus bar a connection or at the Main Breaker. In any case, the problem is something that I doubt you can find or repair yourself, and needs an electrician to troubleshoot and repair as necessary.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    Jul 30, 2012, 08:24 AM
    Have to agree with TK, Could be the Buss the breakers plug onto. A Meter will narrow it down and locate the problem. An Electrician may pull Breaker(s), to see if the buss is burnt.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Power fail without circuit tripping [ 1 Answers ]

Hello, I wired new lights for a basement project. When I flipped on the circuit, the lights came on but my switches were still in the off position. When I flip the switch to 'on' it tripped the circuit. Then I tried having the switches in the 'on' position to start, then I flipped the circuit...

Circuit breakers [ 6 Answers ]

If I have a main disconnect at the pole what kind of breaker box should I put in my quanset To replace the old fuse box,a main lug or main breaker. This is also part my shop. Thanks for any answers, can omeone please help??

Circuit breakers [ 2 Answers ]

It seems so far that our kitchen is wired all on the same circuit. When we use the oven and microwave or the microwave and the toaster oven which is on the other side of the room the breaker trips. That breaker is currently 15amps. Would it be all right to change that breaker to a 25 or 30 amp for...

Circuit breakers [ 2 Answers ]

I would like to up grade the amps going to my garage so I can run my saws and power tools with out dimming my shop lights. I currently have a old style fuse box in the garge feed with 12ga uf cable run off a 20amp circuit breaker in the service panel. My plans are to replace the fuse box with a new...


View more questions Search