    The need for conduit for kaiser Al wire4/0 Awg XLPE 600v XHHW E-90488
    Does xhhw wire for underground application need conduit? It is48" deep trench. The conduit has been broken, about 20", and it's about 100' from the box. Can it be repaired without pulling the wire out? What abou if some water gets into the conduit? Any suggestion will be apreciated.
    Thanks.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 26, 2012, 01:50 PM
    XHHW is not rated to be in direct contact with earth, but is rated for wet locations.

    The damaged conduit needs to be excavated and exposed, the wire pulled out, repair the conduit, and if in perfect condition ,re-install the wire.If the insulation on the wire is damaged, new wire is required.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Size AWG cable and conduit for long runs [ 0 Answers ]

I have a 200amp breaker in box (easement box) next to the utility company power meter, I need to run electrical cable from easement box in underground conduit 200′ to a home where I will have installed new panel and breakers, from the home breaker box need to run 20amp wire in underground conduit...

Amp rating for 4 awg aluminum 600v [ 1 Answers ]

I am trying to find the max amp load for #4 AWG Aluminum 600v cable

6 awg al xlpe 600 V [ 2 Answers ]

I just bought a home that has 6 awg al xlpe 600 volts wire running from the home to a shop 200 ft away. It is running from a 100 amp breaker to a sanother panel box at the shop with a main 100 amp breaker. There are presently one 30 amp double pole breakers and 3 each 30 amp single pole breakers...


View more questions Search