    Weird thermostat
    My heating ac is a little strange in that the tranformer for the ac is outside in the compressor unit. Ever since I switched to a programmable thermostat I have had problem from time to time. There are 5 wires in two cables. Black which is RH and white which is W in one and , red which is RC, yellow which is Y and green which I think is G. I installed a new Hunter 5-1-1 and it worked fine for 2 months. I replaced it under and it worked fine for 2 years. When it did not work it was in controlling the ac. Recently it started acting up working most of the time but every once in a while it wouldn't turn the furnace on usually about 3 pm to 9 pm. For a few days if I reset the thermostat it seemed to work, then this method stopped working. I replaced it with a Honeywell 5-1-1. That work fine for two day now it stopped working. I confirmed that B&W turned the furnace on disconnected G and now at least the furnace started for right now. However fan in the on position does not work. Do you have any idea if G could be causing the problem? Could the furnace be overheating, I can't see that being the problem it's in the attic and it's 16 degrees outside. Even disconnecting the green failed but holding W&B together works. I don't know anything, but could it be too much or too little power from the transformer that is either burning out or not providing enough power to the thermostat?
    labman's Avatar
    labman Posts: 10,580, Reputation: 551
    Uber Member
     
    #2

    Dec 8, 2005, 06:06 AM
    Usually there is a 24 volt AC transformer in the furnace with the secondary winding connected to a red wire running to the thermostat and a blue wire, common, to the gas valve, A/C relay, and fan relay. From the thermostat there will be white wire to the gas valve, yellow to the A/C, and green to the fan. The thermostat is wired to switch the power from the red to the white, yellow, and green as needed with the blue completing the circuit. Most thermostats and furnaces have the contacts labeled R, B or C, W, Y, and G for the corresponding wire colors. It may be wired to have the A/C control wires return to the furnace and its controls and then a second wire goes to the A/C unit. Internal wiring may replace the green wire if the thermostat does not give you the option of fan only or continuous fan. Digital or programmable thermostats may need the blue wire connected to them.

    From the above, you can see why the fan on doesn't work with G disconnected, and holding W and R together causes the heat to come on. Does either type of thermostat have a B or C terminal? What do the black and red connect to at the other end, do they both go out to transformer and connect to the same terminal? With 3 thermostats having gone bad, maybe it is time to look at the transformer. They are fairly cheap, $10-20. If it is an intermittent problem, even testing it for 24 volts might not find the problem. If you do test it, try to test it at the thermostat, red to white. Look at the rating , and get one at least as big, or bigger.
    jmango's Avatar
    jmango Posts: 2, Reputation: 1
    New Member
     
    #3

    Dec 8, 2005, 10:20 PM
    Weird con't
    Ill try the transformer this weekend. Luckily this is the second floor furnace. It does seem to be deteriorating, even holding W to RC doesn't always work. It seems that the funace turns the fan on a lower speed when the heat exchanger come up to temp.
    t_rod95's Avatar
    t_rod95 Posts: 21, Reputation: 0
    New Member
     
    #4

    Mar 1, 2007, 05:34 PM
    Quote Originally Posted by jmango
    My heating ac is a little strange in that the tranformer for the ac is outside in the compressor unit. Ever since I switched to a programable thermostat i have had problem from time to time. There are 5 wires in two cables. Black which is RH and white which is W in one and , red which is RC, yellow which is Y and green which I think is G. I installed a new Hunter 5-1-1 and it worked fine for 2 months. I replaced it under and it worked fine for 2 years. When it did not work it was in controlling the ac. Recently it started acting up working most of the time but every once in a while it wouldn't turn the furnace on usually about 3 pm to 9 pm. for a few days if I reset the thermostat it seemed to work, then this method stopped working. I replaced it with a Honeywell 5-1-1. That work fine for two day now it stopped working. I confirmed that B&W turned the furnace on disconnected G and now at least the furnace started for right now. However fan in the on position does not work. Do you have any idea if G could be causing the problem?? could the furnace be overheating, I can't see that being the problem it's in the attic and it's 16 degrees outside. Even disconnecting the the green failed but holding W&B together works. I don't know anything, but could it be too much or too little power from the transformer that is either burning out or not providing enough power to the thermostat??
    If u give me a day or two I can give u a good answer
    soilsasphalt's Avatar
    soilsasphalt Posts: 4, Reputation: 2
    New Member
     
    #5

    Mar 12, 2007, 03:07 AM
    Readjust your roll out switch next to your flame baffels

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Weird goo [ 9 Answers ]

I have this strange, odorless sticky orange/brown goo slowly oozing from the main sewer pipe out of the house in the basement. It has taken months, possibly years to biuld up, but has become noticeable recently. It looks like candle wax has been dripped on the side of the pipe. I had a plumber...

Help me, my turtle is being weird [ 9 Answers ]

I just bought a turtle, and its breathing really hard, with its mouth open when its on the land part of the tank... Is it panting because its hot??

Weird boyfriend - please help... [ 19 Answers ]

Hi... I'm new at this and need advice... I've been going out with this guy for nearly a yr and a half... but we don't spend more than 2 days togther because we live too far from each other. I have just spent a total of 34hours with him... and he decided he needed space!! ***?? He says he still...

Weird angles [ 2 Answers ]

I am about to replace all the trim in the house and am noticing that the door frames seem to be uneven. By uneven I mean the gap from the corner to trim is larger on the bottom than at the top. We live in a 1 story house this only occurs at a few doors. Would this be poor construction or is the...

Weird guy [ 5 Answers ]

Hello! MY friend likes to wear women's underwear and lingerie. He is straight, but his behaviour is so weird. I don't understand this. Can anyone explain to me? Thanks a lot!


View more questions Search