    Trane XE 1100 heat pump
    I have a Trane Weathertron XE 1100 heat pump which stopped working. The unit makes a noise when I turn on cool on the thermostat which I think might be the compressor. The large fan in the unit does not come on however. I have checked the fuses. I have turned off the thermostat controls and than turned everything on again. What is the likely problem or what else can I check.
    Fred
    hvac1000's Avatar
    hvac1000 Posts: 14,540, Reputation: 435
    Heating & Air Conditioning Expert
     
    #2

    Jul 9, 2012, 07:42 PM
    Quote Originally Posted by fpbock View Post
    I have a Trane Weathertron XE 1100 heat pump which stopped working. The unit makes a noise when I turn on cool on the thermostat which I think might be the compressor. The large fan in the unit does not come on however. I have checked the fuses. I have turned off the thermostat controls and than turned everything on again. What is the likely problem or what else can I check.
    Fred
    If the compressor is running but the fan is not in the outside unit then I would suspect the fan motor capacitor or the fan motor itself. From your description it is very hard to tell for sure without being there.
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #3

    Jul 10, 2012, 01:41 AM
    I would agree with the writer above and I have been in the business for 38 years. If you could test it with a meter you would know; nevertheless, you will most likely need to replace it which means you need to remove the fan and go to an HVAC supply house and buy a new motor with capacitor. You can also have a problem on the outside circuit board which is why you need a meter. There is a relay on that board that controls the outside fan; it turns off the fan when the unit goes into defrost mode when you are using heat.
    fpbock's Avatar
    fpbock Posts: 2, Reputation: 1
    New Member
     
    #4

    Jul 10, 2012, 07:03 PM
    A friend came over and pushed the fan blade on the outside unit. The compressor was running. The fan motor started and ran for about 1 hr before stopping again. Tried spinning the fan but the motor will not kick in. The compressor is definitely running. Is the same copacitor work with both the compressor and the fan motor?
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #5

    Jul 10, 2012, 08:50 PM
    They are two different capacitors, but sometimes they are in the same housing and there are three terminals: a common, fan, and compressor terminal. It's likely you have a blown start winding. You can run the compressor temporarily by putting a sprinkler on the coils to keep them wet (This trick also lowers your electric bill and makes the ac colder) until you replace the fan motor and capacitor. You should test the fan motor with an ohm meter because you could just have an open capacitor and the windings are good on the motor. Check the resistance of the windings and see if you read anything to ground. If you read anything to ground get a new motor and capacitor. Turn off power and find the fan capacitor. It will have two brown wires to it or common and a brown wire. Short the terminals first and measure resistance. If it's good you will measure resistance and it will go to infinity. Switching leads around and it will do it again. If you just get infinity or measure something to ground it's bad and more than likely the motor is bad, too. When you replace the motor you may need a fan puller to get blades off. Make sure to oil motor before installing it with turbine oil which you get at the parts store and get a matching capacitor. Those motors are sealed motors and some are made to be mounted a certain way, up, down, or horizontal. You may have a 1/2, 1/3, or 1/4 hp motor. You can go up, but not down. 1/2 and 1/3 hp are most common on a home ac and 1/4 hp on apartments.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat problems Trane XL 1100 [ 1 Answers ]

We just turned on our heat for the first time of the fall & it only blows cold air. Is there a pilot light? Is there something I can check? Any help would be appreciated. Thanks!

How to wire a trane 900 series thermostat to a trane XL13i heat pump [ 1 Answers ]

How to wire a trane 900 series thermostat to a five wire XL13i heat pump system.

Trane XL20i heat pump requires Trane 900 series thermostat? [ 2 Answers ]

Hi, I was wondering if the Trane XL20i heat pump requires the use of Trane's 900 series thermostat or if a Honeywell VisionPro IAQ thermostat can be used.

Trane xl 1100 heat pump [ 11 Answers ]

I have a trane xl 1100 heat pump split system the outside fan shuts off for no reason all readings are good I have tried 3 different motors with blades that were the right size but still runs about 20 minutes than shuts off, the compressor keeps humming I have had 2 techs look at it but have no...

My trane XL 1100 will no turn on heat [ 1 Answers ]

Yes, I have a trane XL1100 model number YCX036F1M0B. The airconditioning unit is working but not the heater part. The thermostat control will turn on the fan but the spark initiator will not click on and the gas valve will not open. I opened the panel to the electronic controls and is has a red...


View more questions Search