    Bubba14's Avatar
    Bubba14 Posts: 2, Reputation: 1
    New Member
     
    #1

    Jun 26, 2012, 02:47 AM
    Breaker installation in a square d sub panel box
    I installed a 30 amp breaker in a square D box to run my RV. It looks like the neutral bar and ground bar are the same. Other breakers that are in place work fine. When I turn the 30 amp breaker on the lights go bright and then the 30 amp trips. Any suggestionis
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Jun 26, 2012, 04:41 AM
    What kind of wire did you run?
    What kind of breaker is it? Single pole or double?

    I have the suspicion that you installed a 240v circuit to a 120V travel trailer receptacle.

    Can you post a pic of the panel?
    Bubba14's Avatar
    Bubba14 Posts: 2, Reputation: 1
    New Member
     
    #3

    Jun 26, 2012, 09:56 AM
    It is a single pole breaker and it has 120/240 on the front of it. The wire I am using is 12/2
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Jun 26, 2012, 04:57 PM
    One problem is the cable. A 240Vac, 30 amp circuit requires # 10/3 AWG conductors. #12 AWG conductors are only listed for 20 amp.

    Next, how far from the panelboard is this RV?

    In order to feed 240 Vac from the panelboard, you must use a dual 30 amp breaker. A single breaker can only supply 120 Vac.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I need help replacing an old Fuse Box with a new Panel/Breaker Box [ 3 Answers ]

I need to replace my old Cutler Hammer Main fuse box with a new 100 Amp Pannel/breaker box & there are several legs of conduit running from the old fuse box. Two on the bottom, one on the top & one on the side! One coming out from the bottom is the main supply coming from the meter outside with the...

200 amp square d breaker and panel [ 3 Answers ]

Im installing a 200 amp square d panel, but Im having a problem, the main services entrance wires comes in from ground up and the panel is made to feed from top down. I invert the panel but now my main breaker is up side down the on is on the bottom and the off is on top. Here's the question does...

In a spa installation does the GFI breaker go in the disconnect box or main panel? [ 2 Answers ]

In a spa installation does the GFI breaker go in the disconnect box or main panel?


View more questions Search