    Routing electrical cables
    1) can I run 1 12/3 romex cables through a 1/2" hole in studs.

    2) can i run 2 12/2 romex cables in the same 3/4" hole in studs
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #2

    Jun 25, 2012, 08:26 PM
    Let's start with where you live and which code you must follow. Are you asking if the diameter of the romex will fit the size hole or if it is legal to run romex through studs. Not all romex is the same diameter but it should easily fit.
    james parro's Avatar
    james parro Posts: 9, Reputation: 1
    New Member
     
    #3

    Jun 25, 2012, 08:32 PM
    Quote Originally Posted by ballengerb1 View Post
    Let's start with where you live and which code you must follow. Are you asking if the diameter of the romex will fit the size hole or if it is legal to run romex through studs. Not all romex is the same diameter but it should easily fit.
    I live in suffolk county New York and the wires do fit but I would like to no if it is legal
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Jun 25, 2012, 08:56 PM
    It's easier with the larger holes but yes, you can run it that way.
    james parro's Avatar
    james parro Posts: 9, Reputation: 1
    New Member
     
    #5

    Jun 25, 2012, 09:41 PM
    Quote Originally Posted by ma0641 View Post
    It's easier with the larger holes but yes, you can run it that way.
    Thank you
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    Jun 26, 2012, 02:36 AM
    No more that two cables in one hole. More that two will get you into derating of wiring, and no need to go there.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Jun 26, 2012, 04:44 AM
    This is one of the rare times I'll disagree with TK.

    Typically, with #14, #12 & #10 wire, you can run up to four cables in a bored hole.
    For those size wires you do not have to worry about derating until you get to nine CCC's (current carrying conductors). This includes the neutral. This does not however include the neutral of a multi-wire home run (3-wire cable).

    So basically you can have up to four 12/3 home runs in a single hole before derating has any effect.

    There is another stipulation where if the holes are to be firestopped you have to make provisions for two or more cables. My examples above were for general framing.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Jun 26, 2012, 01:02 PM
    I got pinched for more than two years ago, dumb as a rock back then, being lazy now and just threw that out there.

    Did a ton of residential work, back in the day. I try to be careful answering resi questions off the top of my head.

    So I went and checked myself. Stan, I am going on Table 310.15(B)(2)(a), 4-6 gets derated 80%, and since NM cable, I am assuming is used, uses the 60 Deg C column, derating begins there. Maybe that's where I am wrong?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #9

    Jun 26, 2012, 01:14 PM
    Newer NM cable uses THHN conductors inside the cable, so derating begins with the 90 deg C column, which is the actual ampacity of the conductor.

    The 60 deg C limitations and 240.4(D) are after the fact.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #10

    Jun 26, 2012, 04:40 PM
    Stan,

    To the best of my knowledge, even though the newer NMB cables use THHN conductors, they are not identified as THHN on the conductors and are therefore limited to the 60 "C" table.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #11

    Jun 26, 2012, 06:29 PM
    Quote Originally Posted by donf View Post
    Stan,

    To the best of my knowledge, even though the newer NMB cables use THHN conductors, they are not identified as THHN on the conductors and are therefore limited to the 60 "C" table.
    This is not true at all. They are not labeled individually, which is why you cannot strip them out and use them, but they ARE identified as 90 deg THHN so that is what you base derating on.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #12

    Jun 26, 2012, 06:31 PM
    Scroll down for the construction specs: http://www.southwire.com/ProductCata...dcatsheetOEM10
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #13

    Jun 26, 2012, 07:22 PM
    This mouse does not want to be on the dance floor when elephants decide to Tango, but could someone tell me what this means

    dry locations at temperatures not to exceed
    90°C (with ampacity limited to that for 60°C conductors) as specified in the National
    Electrical Code

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

John Deere Belt Routing stx38 M00STXC224963 I need help routing belt [ 0 Answers ]

I need to know how to rout mower belt for STX38 gear #M00STXC224963. Thanks for any help

Too many electrical cables [ 3 Answers ]

I recently replaced the ceiling fan is my very old house. The original fan worked properly, had separate fan and light switches on the fixture, and was controlled by the light switch on the wall which also operated properly. When I dismantled the fan, I found two main electric cables coming from...

The cables of my ac are torn by my dog how can I change the cables? [ 2 Answers ]

The cables of my ac are torn by my dog how can I change does electrical cables?

Electrical Cables [ 1 Answers ]

Instead of using 2runs of 2Core 300Sqmm ( Legth - 1km ) cable for single phase load ( Phase & Neutral ) , can we use 1 run of 4 Core 300sqmm cable (Length -1 Km ) for the same load with 2core for Phase and 2 cores for neutral.


View more questions Search