    Load calculations
    I want to add 10 ceiling recessed lighting fixtures rated at 65W each to an existing 15A circuit. In addition to these the circuit will have 7 outlets, ceiling fan with 4 bulb light kit and porch light. The ceiling fan is older so I am going to guess its power consumption at 75W without the bulbs (new Hunter fans are at 45-55W). The light kit I would estimate at 75W each bulb and the porch light at 75W. Am I overloading a 15A circuit with all this?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Jun 19, 2012, 11:56 AM
    Quote Originally Posted by mauricee View Post
    I want to add 10 ceiling recessed lighting fixtures rated at 65W each to an existing 15A circuit. In addition to these the circuit will have 7 outlets, ceiling fan with 4 bulb light kit and porch light. The ceiling fan is older so I am going to guess its power consumption at 75W without the bulbs (new Hunter fans are at 45-55W). The light kit I would estimate at 75W each bulb and the porch light at 75W. Am I overloading a 15A circuit with all this?
    Let's start this way, please. Because your circuit feeds multiple receptacles you are restricted to an 80% load. Effectivley this means that you sholud not have more than a 12 Amp load on the entire circuit, This is because at any given point in time the load on the receptacles may vary and could cause an overcurrent condition.

    With that out of the way, the load on the lights (65 Watts X 10= 650 Watts)
    (75 Watts X 5 = 375 Watts) I do not trust your guestimate on the fan motor, can you get the amperage off the motor label?

    650 Watts + 375 Watts = 1,025 Watts / 120 Volts = 9 Amps (rounded up.

    That just leaves you 3 amps for all 7 outlets, Way to low!

    Two suggestions:

    1) Add a new 15 ampbranch circuit for 10 new lights.
    2) Convert the entire circuit to 20 amps using 12 AWG copper cable. At 20 Amps you will be allowed to bring the circuit load up to16 Amps.
    mauricee's Avatar
    mauricee Posts: 10, Reputation: 1
    New Member
     
    #3

    Jun 19, 2012, 12:16 PM
    Looks like I will add a 15A circuit for the recessed lighting.

    The fan motor reads .6A 65W. I wasn't far off.

    For future reference how do I figure outlets into load calcs?

    "Because your circuit feeds multiple receptacles you are restricted to an 80% load." Can you elaborate on this? Are there circumstances where you can be at 100% load?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Jun 19, 2012, 12:18 PM
    Just the new lights alone = 33% of a 15 Amp circuit. Add the other lamps and you have minimal possibility of running any decent load on the outlets. Add another 15 Amp circuit for the lights.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Three phase load calculations [ 0 Answers ]

I have three 1.5 kw AC connected in each of the phase since I have 11 KW three phase supply from electricity board. I want to know how much minimum 3-PHASE power backup I should ask THE SOCIETY to enable me run all the three AC on power back up in case the main power fails.

Latent Heat Load - HVAC Load Calculations [ 5 Answers ]

Can someone tell whether latent load contributes to the total cooling load of a building or not.if it does, tell which way, and how it should be looked at during load calculation of a building.Also if possible display a perfect, easily understood definition of latent heat.Thanks

Load calculations for three phase [ 0 Answers ]

Hi There -Three phase 240VAC power supply -Full load current is 240amp. 80amp/phase.. Is there any formula to balance the load current on each phase. Please advise. Thanks.

Electrical Load Calculations [ 4 Answers ]

Electrical Load Calculations with all necessary factors


View more questions Search