    400amp electric panel
    Hi:
    We need to get a larger electric panel. We now have a 150amp plus 2 sub panels with no space and need more breakers for our renovated bathrooms. Some of our current circuits are overloaded and the breakers trip. Our electrician suggests 400 amps.
    How much is a permit and what is involved in changing the panel?
    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Mar 8, 2007, 03:57 AM
    Each city and town sets their permit rates, and they can vary greatly from town to town, state to state. Can be from $10 up to $100. If your city has a website, the permit rates are most likely published there.

    Upgrading any service usually requires first checking with the utility company to confirm the service location is fine, some older services get relocated to meet new requirements of the utility. Each utility also has their own preferences for meter sockets.

    Once the utility is consulted with and a permit is in place, the entire service can be replaced. This includes the conduit/cable riser up the outside of the building if the utility supply is overhead. If underground this may involve replacing the underground cable if a large enough size wire was not installed initially.

    The meter, main disconnect, and main panel is replaced, along with all the heavy cables between each.

    A 400 amp service give a bit more flexibility, since two 200 amp panels is the more practical than one 400 amp panel. Each panel can located strategically to help reduce the length of branch circuits.

    Seems your aware as you mention that more circuits need to be added, just replacing the service is not going to fix any overloaded and tripping branch circuit breakers, just gives you the capacity for more branch circuits, or circuits with heavier loads.

    Has the electrician perform the proper service sizing calculations, or is he just guessing that a 400 amp service is needed. I tell most people that think they want or need a 400 amp service that if you truly need a 400 amp service you most likely could not afford the monthly electric bill.

    Not trying to talk you out of a 400 amp service, just that you may only need a 200 but with more circuit capacity to reduce the load on some circuits.The calcs are quick to do and help confirm what size service is needed. You may be surprised to find you need more than 400 amps!

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

200 amp panel feeding a 100 amp panel roughly 130' away [ 7 Answers ]

Hi all, We are building a apartment above the garage,my question is what size wire do I need to run from the 200 amp panel to the 100 amp panel roughly 130' away? I want to use aluminum wire as I think copper would be to costly. Thanks for your help in advance, Dude :eek:

Electric Force and Electric Field? [ 1 Answers ]

Hello, Can some one explain to me briefly what's the different between electric force and electric field? I am having trouble to make them clear to myself. Thanks you so much. Jack

Kenmore Elite Dryer Toe panel - how to get panel OFF! [ 3 Answers ]

I have a Kenmore Elite Model # 110.600094990 27 inch Electric Dryer - NOW How the heck does one take the Toe Panel Off / or Open this lower section of the dryer? There are two lower edge clips and two upper edge retainers. I CAN NOT get the panel to budge! This is a 7 yr old unit. Thx DAS

Sub-panel [ 2 Answers ]

Hi all, Wednesday the electricians are coming out to swap out the existing 100amp panel with a 200. Which is more practical and economical... installing a sub-panel on the 2nd floor (where the bedrooms & bathroom are) to supply the upstairs or running all the necessary circuits to each room...


View more questions Search