    glm1221's Avatar
    glm1221 Posts: 1, Reputation: 1
    New Member
     
    #1

    Jun 7, 2012, 07:47 PM
    How do I wire a 240v lake water pump gfi breaker
    I have a 4 wire cable leading to a pump in my lake. It has been a long time since I wired it, but I think the neutral(white) and ground are connected to the same point at the pump. I currently have it wired to a standard 20amp 240volt breaker. I recently tried to wire it to a 20amp 240volt gfi breaker, by wiring the white wire to the gfi neutral terminal and taking the pigtail from the breaker to the neutral bus. The breaker trips immediately. I suspect I should not use the white wire, just the ground wire, and still terminate the pigtail at the neutral bus. Also is this the same as wiring a 240volt hot tub. Thanks for your help
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Jun 7, 2012, 08:01 PM
    You won't use the neutral in this case, they wanted to get a better ground and put an unused wire to use, I don't believe you can parallel conductors, unless it is less than 50 Volts, or Larger than 1/0?
    You can secure the unused neutral on the panels neutral bar.
    Handyman2007's Avatar
    Handyman2007 Posts: 988, Reputation: 73
    Senior Member
     
    #3

    Jun 14, 2012, 08:00 PM
    From experience, there are some pump motors that will immediately trip a GFCI. Sump pumps are one type.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Jun 15, 2012, 02:48 AM
    If a new pump trips a GFI, it needs to be returned.
    Handyman2007's Avatar
    Handyman2007 Posts: 988, Reputation: 73
    Senior Member
     
    #5

    Jun 15, 2012, 06:15 AM
    When not wired through a GFI, they run fine. I seriously doubt that at least 20 new sump pumps over the last year were all bad.
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #6

    Jun 15, 2012, 06:34 AM
    What country were they made?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

I am wiring a ductless heat pump with a 20 amp GFI 2 pole breaker ? [ 1 Answers ]

I have 2 questions: since there are 3 terminals on the circuit breaker (2 for hot, one for neutral) how do I wire the breaker with only 2 wires? Second question is I ran 14 gauge wire as per the manufacturers specs. But I understand that 14 is insufficient for a 20 amp breaker. But that's also what...

Can hook up a 110v gfi breaker of one leg ogf a 220v 50 gfi [ 3 Answers ]

I have a 50 amp 220 v gfi hooked up to my hot tub, I ran a 110 v 10 amp gfi off one leg for the underwater light just for extra safety, is this safe to do? I have heard on TV that you can not run 1 gfi off another. Or is this just pertaining ti wall outlets?

How to wiring gfi 50 amp breaker I have red black white copper wire [ 1 Answers ]

How do you wire a 50 amp gfi double pull circuit breaker to a hot tub. From hot tub I have a hot black and red and white neutraul where do these wires go on the breaker.

Lake pump gfci breaker won't trip when test button pushed [ 4 Answers ]

Hi, I have a 15 amp double pole gfci breaker, square d , wired into my panel, it powersa 240 submersible pump in the lake to supply house water. Everything works great, but when the inspector tested the breaker it wouldn't trip as it should. Any ideas? It is a standard submersible with the...

Wiring for pump drawing water from lake [ 3 Answers ]

I am installing a 1 1/2 hp monarch pump to draw lake water for sprinklers and other uses. What type of wire should I bury? I will be running 120 feet from house to pump.


View more questions Search