    Circuit breaker.
    What circuit breaker can you recommend for a welding machine..
    The problem is I don't know the specs..
    smoothy's Avatar
    smoothy Posts: 25,490, Reputation: 2853
    Uber Member
     
    #2

    Jun 6, 2012, 05:40 AM
    Quote Originally Posted by rams99 View Post
    what circuit breaker can you recommend for a welding machine..
    the problem is i dont know the specs..
    You need to know the specs... not only of the welder.. but of the cable being used to wire it up.
    rams99's Avatar
    rams99 Posts: 15, Reputation: 1
    New Member
     
    #3

    Jun 6, 2012, 05:44 AM
    That is the problem... the owner wants me to install wiring for a welding machine.
    He said its only used for round bars..
    Is 60 amp breaker excessive?
    smoothy's Avatar
    smoothy Posts: 25,490, Reputation: 2853
    Uber Member
     
    #4

    Jun 6, 2012, 05:48 AM
    Quote Originally Posted by rams99 View Post
    That is the problem... the owner wants me to install wiring for a welding machine.
    he said its only used for round bars..
    is 60 amp breaker excessive?
    Without any other information... yes. You really HAVE to have other information. Such as at a minimum.

    What size wiring are you intending to use... what is the voltage of the welder.. and what is its maximum amp capacity.

    You HAVE to know those things or you can create a hazardous condition where a fire might result.
    rams99's Avatar
    rams99 Posts: 15, Reputation: 1
    New Member
     
    #5

    Jun 6, 2012, 05:55 AM
    I'am intending to use no. 10 wire with a 60 amp breaker.
    Or just wait till he can give me other specs of the welding machine...
    rams99's Avatar
    rams99 Posts: 15, Reputation: 1
    New Member
     
    #6

    Jun 6, 2012, 06:45 AM
    He said it is a 200 amp welding machine.
    smoothy's Avatar
    smoothy Posts: 25,490, Reputation: 2853
    Uber Member
     
    #7

    Jun 6, 2012, 07:09 AM
    I believe NEC (National electric Code) calls for a #6 (6 guage) copper wire for a 60 amp circuit I assume the distance is fairly short... or that wire size will need to be larger depending on distance if its not.

    I'm an Electronic Engineer, not a Master Electritian... so if I'm wrong someone will correct me.

    Change your wire size from a #10 to a #6 (larger) and a 60 Amp breaker should be good for that application.
    rams99's Avatar
    rams99 Posts: 15, Reputation: 1
    New Member
     
    #8

    Jun 6, 2012, 07:20 AM
    #6... got it... its only half a meter distace by the way..
    Thanks..
    smoothy's Avatar
    smoothy Posts: 25,490, Reputation: 2853
    Uber Member
     
    #9

    Jun 6, 2012, 07:24 AM
    Quote Originally Posted by rams99 View Post
    #6... got it... its only half a meter distace by the way..
    thanks..
    Half meter is very close... has to be much longer than that before distance becomes a factor in sizing.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #10

    Jun 6, 2012, 08:29 AM
    Here is a spec sheet for a plain vanilla 230 volt input welder with a 200 amp output.

    Northern Industrial Welders Arc 200 230 Volt Stick Welder — 200 Amp Output | Arc Welders | Northern Tool + Equipment

    Shows it draws 41 amps at the 230 volts.

    So, choosing the 60 amp circuit for a typical welder is fine.

    I do have to say I am glad your asking the question, your comment that you had planned to use #10 wire on a 60 amp circuit breaker leads me to believe your not an electrician.

    #10 wire on a circuit amp circuit would be a serious hazard.

    Smoothy is correct, #6 copper wire can be used on a 60 amp circuit.

    Before any electrical circuit is installed, the installer should have the specifications of the device, appliance, or machine that needs power.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #11

    Jun 6, 2012, 01:29 PM
    Quote Originally Posted by rams99 View Post
    That is the problem... the owner wants me to install wiring for a welding machine.
    he said its only used for round bars..
    is 60 amp breaker excessive?
    Quote Originally Posted by rams99 View Post
    I'am intending to use no. 10 wire with a 60 amp breaker.
    Are you an electrician?
    What is your profession?

    I am getting the impression that you really have no place doing wiring for customers for pay.
    rams99's Avatar
    rams99 Posts: 15, Reputation: 1
    New Member
     
    #12

    Jun 6, 2012, 08:55 PM
    I'm still a student.
    but I know about installing light and outlets.
    our school haven't really taught us about the higher ampacity loads yet.
    and I'm doing this for experience only.. ^^^
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #13

    Jun 7, 2012, 04:18 AM
    Quote Originally Posted by rams99 View Post
    I'm still a student.
    but i know about installing light and outlets.
    our school haven't really taught us about the higher ampacity loads yet.
    and I'm doing this for experience only..^^^
    The you should NOT be doing it. You are obviously not nearly experienced enough yet and need to learn from someone in the field before venturing out on your own. Even for something as seeming small as this.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #14

    Jun 7, 2012, 05:12 AM
    Exactly, no student should be doing ANY electrical work without proper supervision.

    A little bit of knowledge is dangerous.

    You intending on using #10 wire on a 60 Amp breaker shows that you have not gotten to #10 wire ampacity in your course study.

    I am glad you asked the question, I need to inform you that you need to stay in school, and never do any electrical work for anyone until you have completed the course, completed your apprenticeship, and obtain the proper license.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

Why vacuum circuit breaker is prefer on oil circuit breaker ? [ 1 Answers ]

Why vacuum circuit breaker is prefer on oil circuit breaker ?

I have a Murray circuit breaker panel and want to add a circuit for a 3 prong elec dr [ 3 Answers ]

I have an electric 3 pronged dryer that I want to add a circuit for on my Murray Circuit Panel. What kind of switch do I need?

Circuit Breaker trips because two bathrooms and master bedroom on same circuit [ 6 Answers ]

Some electrician committed a blunder in my opinion about 17 years ago. The master bedroom and two full bathrooms are all on the same circuit. If two hair dryers are used at the same time, it will trip the breaker every time. In figuring out what amperage would be required for two hair dryers and...


View more questions Search