Ask Experts Questions for FREE Help !
Ask
    closetpic's Avatar
    closetpic Posts: 10, Reputation: 1
    New Member
     
    #1

    Jun 4, 2012, 01:48 PM
    Light fixture
    I have just installed a dimmable recesssed light fixture and put it on a dimmer, but the switch will not control the light, it just stays on. Wired as black to black and a red from the fixture to the white. A red and white wire has been capped off? What do I need to do?
    dogdeville's Avatar
    dogdeville Posts: 69, Reputation: -4
    -
     
    #2

    Jun 4, 2012, 02:02 PM
    I don't think your switch is wired right
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #3

    Jun 4, 2012, 02:11 PM
    Whites need to remain intact.
    I would test without dimmer and have it work with a switch first, If you did that and when you hook the dimmer up and remains on, it is a bad dimmer.
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #4

    Jun 4, 2012, 02:18 PM
    .
    Wired as black to black and a red from the fixture to the white. A red and white wire has been capped off? What do I need to do?
    Are you talking about the wiring at the switch or wiring at the light fixture?
    closetpic's Avatar
    closetpic Posts: 10, Reputation: 1
    New Member
     
    #5

    Jun 4, 2012, 02:51 PM
    Quote Originally Posted by hkstroud View Post
    .

    Are you talking about the wiring at the switch or wiring at the light fixture?
    Black from power source and black from switched are twisted together with black from fixture. White from power source is twisted with white from the fixture. The switch has a black, red and then a red and white wire which is capped off. The black is to the black and the red is to the white.

    Charlie
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #6

    Jun 4, 2012, 03:42 PM
    Sounds like your dimmer requires a neutral, If so, black likely goes to constant hot, the white to neutral, and the red would go the light.
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #7

    Jun 4, 2012, 04:42 PM
    Quote Originally Posted by closetpic View Post
    I have just installed a dimmable recesssed light fixture and put it on a dimmer, but the switch will not controll the light, it just stays on.
    Quote Originally Posted by closetpic View Post
    Black from power source and black from switched are twisted together with black from fixture.
    I think THIS is your answer, no?

    If the constant hot and the switched hot are twisted together wouldn't that obviously keep it on all the time?
    closetpic's Avatar
    closetpic Posts: 10, Reputation: 1
    New Member
     
    #8

    Jun 4, 2012, 05:19 PM
    It maybe better if I take this matter from the top..
    I have run a bx cable fron an existing outlet box. I have attached the black power wire to the black wire from the bx and did the same to the white wire. Then I attached the other end of the bx to the fixture black to black and white to white. With more bx cable for the switch (also connected black to black and white to white),Then for the switch I attached the black from the bx to the black coming from the dimmer. I then attached the red coming from the dimmer to the white from the bx. The dimmer has a black wire, a red wire, and a red&whit wire that is capped off.
    Light stay on and switch will not allow off & on. What did I do wrong?
    closetpic's Avatar
    closetpic Posts: 10, Reputation: 1
    New Member
     
    #9

    Jun 4, 2012, 05:21 PM
    Quote Originally Posted by Stratmando View Post
    Sounds like your dimmer requires a neutral, If so, black likely goes to constant hot, the white to neutral, and the red would go the light.
    The only red I have is coming from the dimmer and it is attached to the white cominfrom the bx. The dimmer does have a red&white wire that I habe capped off.. . Please help
    closetpic's Avatar
    closetpic Posts: 10, Reputation: 1
    New Member
     
    #10

    Jun 4, 2012, 05:37 PM
    Quote Originally Posted by closetpic View Post
    Black from power source and black from switched are twisted together with black from fixture. White from power source is twisted with white from the fixture. The switch has a black, red and then a red and white wire which is capped off. the black is to the black and the red is to the white.

    Charlie
    I have run bx from an existing outlet. The black from the power source is attached to the black from the bx and same for the white. I then attached the black from the bx from power source and the black from the bx for switch to black on the fixture. White from power source is attached with white form switch to white from the fixture. Lastly the switch has a black wire. A red wire and a red&white wire. I connected black wire from switch to the black from the bx and the red from the switch to the white from the bx. The red&white from the switch is capped off... Please help
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #11

    Jun 4, 2012, 07:20 PM
    Red/white and red&white can be taken a couple of ways.
    Red/white, or red w/white is usually considered 1 wire.
    Red & white is usually considered 2 wires.

    What make and model of switch do you have?
    Will a regular light switch work?
    hkstroud's Avatar
    hkstroud Posts: 11,929, Reputation: 899
    Home Improvement & Construction Expert
     
    #12

    Jun 4, 2012, 09:09 PM
    I have run bx from an existing outlet. The black from the power source is attached to the black from the bx and same for the white.
    The way I read that is you ran BX cable from an existing outlet to the ceiling box for the light. You connected the black of the outlet to the black of the BX cable. You attached the white of the outlet to the white of the BX.

    I then attached the black from the bx from power source and the black from the bx for switch to black on the fixture. White from power source is attached with white form switch to white from the fixture.
    The way I read that is that in the ceiling box you attached the black of the BX cable from the outlet to the black of a BX cable to the switch and also to the black of the light fixture. You attached the white of the cable from the outlet to the white of the cable going to the switch and to the white of the flight fixture.

    If I am reading correctly you have wired a complete circuit from the outlet to the light (and to the switch location). Therefore not mater what you do at the switch, the light will burn.

    Appearently the dimmer switch you have purchased is a 3-way dimmer switch.

    At the ceiling box.
    Attach the white from the outlet to the white of the light fixture.
    Attach the black from the outlet to the white going to the switch.
    Attach the black from the switch to the black of the light fixture.

    At the switch location,
    Attach the white of the cable coming from the ceiling to the black of the switch.
    Attach the black of the cable coming from the ceiling to the black of the switch.
    Leave the red/white from the switch capped off with a wire nut.
    closetpic's Avatar
    closetpic Posts: 10, Reputation: 1
    New Member
     
    #13

    Jun 5, 2012, 07:27 AM
    Quote Originally Posted by hkstroud View Post
    The way I read that is you ran BX cable from an existing outlet to the ceiling box for the light. You connected the black of the outlet to the black of the BX cable. You attached the white of the outlet to the white of the BX.



    The way I read that is that in the ceiling box you attached the black of the BX cable from the outlet to the black of a BX cable to the switch and also to the black of the light fixture. You attached the white of the cable from the outlet to the white of the cable going to the switch and to the white of the flight fixture.

    If I am reading correctly you have wired a complete circuit from the outlet to the light (and to the switch location). Therefore not mater what you do at the switch, the light will burn.

    Appearently the dimmer switch you have purchased is a 3-way dimmer switch.

    At the ceiling box.
    Attach the white from the outlet to the white of the light fixture.
    Attach the black from the outlet to the white going to the switch.
    Attach the black from the switch to the black of the light fixture.

    At the switch location,
    Attach the white of the cable coming from the ceiling to the black of the switch.
    Attach the black of the cable coming from the ceiling to the black of the switch.
    Leave the red/white from the switch capped off with a wire nut.
    I have wired it exactly as you have written above and now there is no light...
    At the switch location, please confirm what you have written for steps 1 & 2?
    The red/white wire is still capped off.
    Thanks, Charlie 773 / 425-8024
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #14

    Jun 5, 2012, 07:37 AM
    Did it come with instructions, does it have a name, model # or anything? Or can you tell what the re/white wire does?
    Is this Compact Fluorescent?
    closetpic's Avatar
    closetpic Posts: 10, Reputation: 1
    New Member
     
    #15

    Jun 5, 2012, 08:26 AM
    Quote Originally Posted by Stratmando View Post
    Did it come with instructions, does it have a name, model # or anything? or can you tell what the re/white wire does?
    Is this Compact Flourescent?
    Yes it came with instructions, but they read as if I'm replacing a fixture, I'm not it is a new fixture from a current outlet box. It is a Catalina Lighting fixture model# 244196. A 3"GU10 brushed steel downlight, and they have not responded in a week now. The instruction say nothing about red/white wire, but a sticker on the red/white wire says to leave the blue cap on for single pole installation. Please help... It looks like your previous directions were taking it from the top and I redid everything, but now no light ta all..
    closetpic's Avatar
    closetpic Posts: 10, Reputation: 1
    New Member
     
    #16

    Jun 5, 2012, 08:28 AM
    Quote Originally Posted by closetpic View Post
    I have wired it exactly as you have written above and now there is no light...
    At the switch location, please confirm what you have written for steps 1 & 2?
    The red/white wire is still capped off.
    Thanks, Charlie 773 / 425-8024
    At the switch location instructions, it seems like step 1 & 2 are to attach to the black from the swith, it that true?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #17

    Jun 5, 2012, 09:02 AM
    Then we don't have to worry about the capped wire.
    Remove Dimmer, and you need to try to make it work with a regular switch.
    When you remove the switch, connect those 2 wires to the dimmer.
    If the light stays on, or won't come on with the dimmer, the dimmer is bad.
    I know the base of the GU 10, but thought most are compact fluorescent, Are you using a compact fluorescent bulb, and or is the dimmer for CFL?
    closetpic's Avatar
    closetpic Posts: 10, Reputation: 1
    New Member
     
    #18

    Jun 5, 2012, 09:31 AM
    Quote Originally Posted by Stratmando View Post
    Then we don't have to worry about the capped wire.
    Remove Dimmer, and you need to try to make it work with a regular switch.
    When you remove the switch, connect those 2 wires to the dimmer.
    If the light stays on, or won't come on with the dimmer, the dimmer is bad.
    I know the base of the GU 10, but thought most are compact flourescent, Are you using a compact flourescent bulb, and or is the dimmer for CFL?
    You are the MAN... I cannot express the depth of my gratitude for you regarding such a frustrating problemthat is now SOLVED...

    It worked with a regular switch and worked again with a another dimmer... You deserve major cudos.. THANKS THANKS AND THANKS AGAIN
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #19

    Jun 5, 2012, 12:07 PM
    Good Deal, great to get it behind you.
    Thanks for hanging in there, and the reply.
    Take Care

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Light fixture shorted out, replaced fixture, now no power [ 4 Answers ]

In my bathroom, I have 1 grounded receptacle, & (1) 2 wire light switch that controls the 4 bulb light fixture. This is on a circuit with my upstairs lights & outlets, which all work with no problem. The bathroom receptacle has never worked, I replaced it after moving in house 10 years ago, & it...

How to change a pull string light fixture to a wall switch controlled light. [ 2 Answers ]

How do you change a pull string light fixture to a new light fixture with a wall switch. I have two wires running to the existing string light and am not sure what to do with those wires. I plan to change the light as well.

I have connected the light ceiling fixture but the light remain on cannot switch off [ 7 Answers ]

I have two black wires, one red, one wihite out of the box. I have connected the two blacks with the black fixture, and white with the white fixture wires. The red is not connected. The light (florescent U-tube light) comes on, but stays on, regardless of the switch being in the on or off position,...

How to change a pull chain fixture to a fluorescent light fixture with a switch ? [ 1 Answers ]

I would like to install a switch for a pull light fixture. The only power is from the light fixture, but I want to put a light switch on the wall as I enter the room, Can you help ?

Hamton Bay outdoor light fixture... how to replace a dead light bulb. [ 0 Answers ]

I have to see if one of the glass panels slides up or down or left and right. It does not appear that the top or bottom is removable. Don't have instruction guide... don't know the model number


View more questions Search