    Electrical wire size 125 amp sub panel
    I have a 125 amp meter panel and want to run a 100 amp service to a panel in my shop. The distance is approx 50 feet. What size conductors are required?
    Thanks, dave
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    May 8, 2012, 03:49 PM
    As a minimum , use 3 - #2 Alum XHHW insulation and 1 - #4 Al XHHW as equipment ground in 1-1/4" conduit, complete with elbows , fittings, and connectors from panel to panel.

    Technically, need to use a 90 Amp circuit breaker. Many inspectors allow a 100 amp breaker used.
    davheb's Avatar
    davheb Posts: 3, Reputation: 1
    New Member
     
    #3

    May 8, 2012, 07:45 PM
    I'm only thinking of using copper!!
    davheb's Avatar
    davheb Posts: 3, Reputation: 1
    New Member
     
    #4

    May 8, 2012, 07:46 PM
    I'm only considering copper
    Washington1's Avatar
    Washington1 Posts: 798, Reputation: 36
    Senior Member
     
    #5

    May 8, 2012, 08:48 PM
    I agree with TK. To add: Although 50 feet is not that far, it "may be” possible to need more than four bends to complete your conduit run. Per code:There shall not be more than the equivalent of four quarter bends (360 degrees total) between pull points. An example of a pull point would be and electrical box.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #6

    May 9, 2012, 02:32 AM
    Then 3- # 3 and 1- #8 copper THHN/THWN.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Size Wire for 100 Amp Garage Sub-panel [ 4 Answers ]

What type and size wire, in PVC conduit, for 100 amp 120/240 volt sub-panel in free standing garage/workshop 120 feet from main panel? I assume 1/0 aluminum will be cheaper than #1 copper and ground must insulated. What size ground. What size conduit? Will 2" conduit be worth the additional...

What size wire feeding a 60 amp sub panel? [ 1 Answers ]

The sub panel is 100 ft away from the main 200 amp panel.There will NOT be any machinery (welders, table saws, compressor or any other motors except the washer and a secondary refrigerator). I'm thinking 4-#6 THHN wire enclosed in 1" armor cable in attic then buried in 1" pvc sch 40 and protected...

Sub Panel AMP Size and Supply Wire Size [ 1 Answers ]

I would like to install a sub panel in my garage I was told to run 6/3 Romex to supply the sub panel and have done so. The run is about 65 feet and I am now wondering after reading this site what is the max I can get for this size wire? I plan to supply a compressor (20 amp) and the garden...

125 amp sub panel 250' away wire size [ 5 Answers ]

I have a 400 amp service in my home and will be running a line to my shop with a total run of 250' to feed a sub panel 125 amp service. What wire size is the 250' run? Would a 100 amp service be the same wire size? I would like to run copper wire, is aluminum that much less expensive? Any other...

100 amp sub panel wire size [ 2 Answers ]

I now have the 100 amp breaker installed in my load panel. I will run wiring from the load panel to a 100 amp sub-panel in an unground 80 schedule PVC. I believe I need to use #2 wire for the hots and the neutral. If this is correct, then what size ground do I use? Number 6? The sub- panel...


View more questions Search