    Electrical switch (15amp) question icw 12/2
    My house is wired with 12/2 Romex and 20 amp circuit breakers. However, I happened to notice that the switches that were used have a 15amp label. I was surprised to find that, I thought it would indicate 20amp. I checked other switches and they were all the same. Is it normal for electricians to use 15amp switches with 12/2 (20amp) circuits? I went to Home Depot and found that all the switches for sale were 15amp. Do they make or sell 20amp switches? I couldn’t find any.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Apr 23, 2012, 12:45 PM
    There are 20amp switches, Leviton makes them. However unless you are switching heavy loads, they are not necessary. Note that you most likely have 15 amp outlets too, but they are allowed on a 20 amp. Circuit. If your outlets don't have a
    "tee" shaped inlet on the receptical, you have a 15 amp outlet.
    ._
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #3

    Apr 24, 2012, 04:29 AM
    I agree with ma0641,
    The electrical code generally allows a 15 ampere rated switch to be used as long as the load is connected to does not exceed some percentage of it's rating. The code section is 404.14.
    For most (almost all) things that one would be connecting to in a residential application, a 15 ampere rated switch can be used with loads not exceeding the ampere rating of the switch.
    Now there are some types of applications where the load is limited to 50% of the ampere rating of the switch (Inductive loads) and motor loads where the load is limited to 80%.
    This was a good question...

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Electrical switch [ 4 Answers ]

Switch on DC07 turns on power but you have to keep hand on it otherwisw power cuts out.

Electrical transfer switch [ 4 Answers ]

I have a 2 pole 60 amp Manuel transfer switch. I am installing a 2 pole 60 amp breaker in my main panel with #6 wire ( 2 hots and a neutral plus ground) to feed the 2 pole 60 amp transfer switch. From the main lugs on the 2 pole 60 amp transfer switch I am feeding a sub panel with #6 wire ( 2...

Electrical switch [ 1 Answers ]

I need an enclosed rotarty switch (enclosed), it fits inside the tubing of the halagen lamp 120v, the wires on the switch must be enclosed to prevent shorting out inside the tube so it doesn't short out. Where can I find a replacement, zing ear part #136609 Thank you

Electrical switch [ 15 Answers ]

I have a swtich that controls an outlet in a bedroom that was not working. I replaced the swtich and the outlet. When I plug the lamp into the outlet and turn the switch on it trips the circuit break for the electric in that room. Can anyone tell me how to fix this or what is causing this? ...

Electrical Switch that controls nothing [ 5 Answers ]

Trying to install some track lighting so decided to do some investigating. There is a light switch in the room that controls nothing in the house. I've tested every outlet on the circuit and no change. Opened it up and see that there are 3 wires. One white, one black, one red. The black and...


View more questions Search