    3 phase 208 volt panel 11000 kw what size breaker to use
    I have a 3 phase 208 volt 11kw oven. What size breaker should I use.
    Is it 208/11000 which would be 50 amp
    Or 240/11000 which is 45 amp.
    Current power source is 208 volts and currently has # 6 wire
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Apr 5, 2012, 02:43 AM
    If in the USA, the breaker and feeder needs to be rated 25% higher than the load.

    11000 watts / (208 * 1.73) = 30.5 Amp load * 1.25 = 38.125 amp circuit rating.

    A 3 pole 40 amp breaker using the existing #6 wire will work fine.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Can you operate a light fixture rated for 240 volt, on 208 volt single phase? [ 1 Answers ]

I have an old street light that has a multi tap ballast, the only markings that I can read on the wires are 240volt. My system is 3phase 208 volt and I was told that I could get a 2 pole breaker and the fixture would work. Is this the case?

Can you run a 208 volt heating panel on 240 volt electrical supply [ 1 Answers ]

I have a baseboard electric heater that is 208 volts. My power supply is 240 volts. What will happen if I try to run m y 240 volt electrical supply to my 208 volt electric baseboard heater?

Will a 208 volt 3 phase mixer work off a 240 volt 3 phase service? [ 7 Answers ]

I have 240 volt 3 phase service and I have a 208 volt 3 phase mixer. Can I hook it up to the 240 volt 3 phase service? Also I have a 208 volt 3 phase oven will it work for that as well?

208 volt3 phase why to single phase 120 volt [ 4 Answers ]

Supply is from 75 kva transformer, 3 phase delta /y three wire feeding a 30 amp breaker. 100 feet down stream is a junction box that I want to tap and produce a 120 v single phase ( 20 amp CB) supply. The junction box feeds a 6 amp motor

3 phase 208 volt/120 volt .load [ 1 Answers ]

I am trying to hook up a commercial espresso machine which has a 220 line. My existing electrical box is a 3 phase 208 volt/120 volt. Would this be sufficient to handle this?? Thank you


View more questions Search