    Lennox elite cb30m 65 1p circuit breaker position
    I have just moved house, it has a Lennox Elite CB30M 65 1P heat pump. There are two circuit breakers on the front, the left one is off and the right one is on. We are trying to find the correct settings for A/C in the summer and Heat in the winter. Anyone have any ideas?
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #2

    Apr 3, 2012, 07:18 PM
    Circuit breaker should be a double pole and both should be on. Are you sure you mean circuit breaker?
    chubtor's Avatar
    chubtor Posts: 5, Reputation: 1
    New Member
     
    #3

    Apr 4, 2012, 07:34 AM
    Thank you for your reply. Yes they are definitely two Square D circuit breakers mounted near the top left of the appliance, they have no markings and no indication as to what they do, I tried looking at a schematic but it seemed to be generic to lots of Lennox models and I couldn't figure out the function of the two that I have. As it is a heat pump, could one of them be for the auxiliary heater perhaps? I don't know I am just guessing. At the moment the unit is working (ie blowing cold air) with the left one on and right one off and yes that is the reverse of what I said in my original post - I got it wrong last time.

    Any clue that you can give regarding the function of these two circuit breakers would be appreciated.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #4

    Apr 4, 2012, 09:14 AM
    I have never seen a heat pump run on 120VAC. Strip heaters draw a lot of current. This could be a safety disconnect as code requires such but not sure as to what the 2 are.
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #5

    Apr 4, 2012, 09:15 AM
    You may find that the main breaker panel has the 240VAC. These could be for the fan and possibly the crankcase heater. Where are you located?
    chubtor's Avatar
    chubtor Posts: 5, Reputation: 1
    New Member
     
    #6

    Apr 4, 2012, 11:01 AM
    I am in South Austin, Texas
    ma0641's Avatar
    ma0641 Posts: 15,675, Reputation: 1012
    Uber Member
     
    #7

    Apr 4, 2012, 11:30 AM
    I would go to the Lennox web site and either post the same question of see if they have a chat line. Maybe you can download a PDF manual. GoodLuck.
    chubtor's Avatar
    chubtor Posts: 5, Reputation: 1
    New Member
     
    #8

    Apr 4, 2012, 12:02 PM
    Thank you, I will try that.
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #9

    Apr 11, 2012, 06:23 AM
    Those breakers are for two different banks of heat strips. Some people like to run 20 kw and others like 45 kw. If you have deep pockets turn both on, otherwise use only 20 kw. The one that's on is probably the main one, so I would mark it. To get really good efficiency unplug W1 and you will only use the heat pump for heat. W1 brings in heat strips when it's not heating fast enough like when the set point is more than 2 degrees than room temp. For example, if you set the heat for 70 degrees and it's 67 degrees the heat strips (emergency heat) will come on for a few minutes until it's 68 or 69 degrees, then they drop out. Heat pumps have at least two stages of heat and sometimes three, as in your case, probably. At least you can wire yours to have three stages where heat strips would come on when W1 (2nd stage) and W2 (3rd stage) are energized in t-stat. Due to your location I cannot see where you would need that much heat to get the house to 68-70 degrees.
    chubtor's Avatar
    chubtor Posts: 5, Reputation: 1
    New Member
     
    #10

    Apr 11, 2012, 07:31 AM
    Thank you for your reply, that sounds pretty logical to me however I am no sure what you mean about unplugging W1. Could you be a bit more explicit please. What exactly is W1?
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #11

    Apr 11, 2012, 12:20 PM
    W1 is on the thermostat sub base where the wires attach and it is the white wire going into the air handler. If it is temporarily disconnected or a switch is put on it so you can turn it off until needed such as when you have a bad ice or snow storm you will not use heat strips which run up your electric bill. You can wire in a simple toggle switch that will go into a 1/2 " hole on side of unit to do the job. Then the white t-stat wire will come from t-stat into switch and leave switch and go into W1 terminal where it is now. It's really easy to do and will save a lot of money unless you keep the t-stat at the same temp all the time. It's most helpful if you want the temp to drop more than 3 degrees while the family is away or you are using a set back t-stat and do the same.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Theory of vacuum Circuit Breaker & sf6 circuit breaker [ 15 Answers ]

I want to know about the basic Theory of vacuum Circuit Breaker & sf6 circuit breaker

I have a Murray circuit breaker panel and want to add a circuit for a 3 prong elec dr [ 3 Answers ]

I have an electric 3 pronged dryer that I want to add a circuit for on my Murray Circuit Panel. What kind of switch do I need?

Lennox a/c compressor won't turn on after main circuit breaker of house tripped [ 2 Answers ]

Not sure if it's associated but main circuit breaker of my house tripped the other night. (I don't know why!) A few hours later after resetting it I noticed a/c not working properly. I know very little about A/C. Could something have simply tripped in unit that I need to reset. It's a Lennox Elite...