    New bathroom wiring
    Hi,

    I am wiring a new bathroom. I have the following to install:
    3 recessed lights, 1 GFCI outlet, 1 Nutone exhaust fan, 2 sconce lights

    Can I do the following?
    Run 12-2 romex from a 20 amp breaker to the GFCI outlet
    Run 12-2 from the GFCI outlet to a 2 gang switch box
    Control the sconce lights and 3 recessed lights from one switch
    Control thre exhaust fan with the other.
    creahands's Avatar
    creahands Posts: 2,854, Reputation: 195
    Ultra Member
     
    #2

    Mar 8, 2012, 07:00 PM
    I am not an electrician, but I believe you need one circuit for GFCI outlet and another for the lights. I would check code in your area.

    If wired the way you stated and GFCI pops you will lose the lights.

    Chuck
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #3

    Mar 8, 2012, 07:16 PM
    "Control thre exhaust fan " is this a fan only, no light and no heater? Romex is a brand of wire made by Southwire, what type are you using? I am with Chuck, run 2 separate circuits for a bath with receptacle and lights separate.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #4

    Mar 9, 2012, 01:40 PM
    There are several ways to wire a bathroom.

    The NEC requires that the bathroom receptacle be on a 20 amp (#12/2 cable) GFCI protected circuit. The circuit can be protected at the breaker by using a GFCI breaker or, to install a GFCI protected receptacle <preferred method>.

    In my opinion this the best way. Separate the lighting and fan on one 15 amp circuit. A run a separate 20 amp circuit to the GFCI corntrolled receptacle. That way if the GFCI trips you still have the lights on.

    The NEC does allow for a single 20 amp to supply one entire bathroom including the GFCI receptacle. If you choose to do the bathroom with one 20 amp circuit, then you have to make sure the last thing on thecircuit is the GFCI receptacle, otherwise, if the GFCI recptacle trips, you will be standing in the dark
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #5

    Mar 9, 2012, 02:31 PM
    The GFI does not have to be last on the circuit. A GFI can be wired to only the LINE terminals so it is not protection anything downstream.

    Unless there is a heater on the circuit, one 20A circuit should be fine for the whole bathroom.

    daisydakota, your plan seems fine to me.
    The fan is not over the tub or shower, is it?
    daisydakota's Avatar
    daisydakota Posts: 2, Reputation: 1
    New Member
     
    #6

    Mar 12, 2012, 04:12 PM
    The fan will not be over the shower, rather it will be in the center of the room. What do you mean by the LINE terminals?
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #7

    Mar 12, 2012, 04:54 PM
    On a GFCI receptacle there are two sets of terminals.

    The "Line" side, which is where the supply going into the receptacle. It this circuit and anything connected to the receptacle that is protected by the GFCI.

    The "Load" side is where you connect the conductors that you want to protect downstream of the GFCI receptacle.

    If you only want the receptacle protected, only connect conductors to the "Line"side.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bathroom wiring [ 2 Answers ]

I have 2 bathrooms, both with outlets, can I run the power to a GFC in the first bathroom and then to a regular outlet in the second bathroom? Does this conform to code, or must I put them on separate circuits each with a GFC outlet?

Bathroom Wiring [ 1 Answers ]

I am remodeling a bathroom including installinf GFCI outlets, new lights, vent and switches. Can I use 12/2 NMB wiring or does it need to be NMC?

Bathroom wiring [ 1 Answers ]

I am wiring an elecric towel rail & blanket underfloor heating in a bathroom, I know this has to be done to IEE standards trough a flex outlet & an external fused connection unit. I just looking for conformation on what height I should put the flex out let in the bathroom. I am in Scotland, I...

Bathroom Wiring [ 1 Answers ]

I have read as many bathroom posts as I could find but still have a specific question. First I want to reiterate what I have gathered. Please verify the following for correctness. 1. Outlets and lights must be on separate circuits in a bathroom. 2. All outlets must be GFI protected by breaker...

Bathroom wiring [ 2 Answers ]

First question was answered somewhat,here's the scenario,remodeling bathroom,ran 20 amp service,wired in fan/light .light is wired for use by itself.Fan,light in tub,shower,vanity light and three outlets [one outlet is gfci,20 amp rating. Would like to use 15 amp switch for general light,this is in...


View more questions Search