    Carrier CD5BXA036000AAAA fan won't shut off; heat and A/C won't turn on
    A few days ago everything worked fine. I left for a few hours and when I came home that night only the fan worked and it wouldn't shut off. The thermostat looked to have gone mad, the temperature reading on the thermostat was changing up and down within three degrees despite that fact that the air temp. Coming out of the vents wasn't changing. I swapped out the thermostat, because I hated the old one, and was hoping that would solve my problem. Predictably it did not.
    thermalmedics's Avatar
    thermalmedics Posts: 153, Reputation: 13
    Junior Member
     
    #2

    Mar 11, 2012, 07:56 AM
    A couple of questions:

    1.When you say fan stays on do you mean the indoor blower motor with air coming out at the registers?

    2.Is the unit a split system or package unit?

    3. If a split system does the outdoor unit (condenser fan and compressor) come on?

    4.Can you turn off the thermostat completely and have the fan stop blowing?
    thermalmedics's Avatar
    thermalmedics Posts: 153, Reputation: 13
    Junior Member
     
    #3

    Mar 11, 2012, 08:20 AM
    Sorry, double post
    Eric_N's Avatar
    Eric_N Posts: 2, Reputation: 1
    New Member
     
    #4

    Mar 12, 2012, 11:42 AM
    1. Yes, it's the indoor blower.

    2. It is a split system.

    3. The outdoor unit doesn't turn on at all.

    4. I haven't tried it with the thermostat unwired, but with it set to off the fan continues to blow.
    thermalmedics's Avatar
    thermalmedics Posts: 153, Reputation: 13
    Junior Member
     
    #5

    Mar 12, 2012, 10:14 PM
    One troubleshooting tip is to take a small wire nut and connect the red and green wires on the thermostat (after removing the t-stat plate first).

    Just keep all the wires nice and separated at first then go red to green.
    1. Does the indoor fan come on and then turn off when the wires are separated?

    If yes:

    Now take red, yellow and green and connect with wire nut.

    2.Does outdoor unit run with indoor blower motor. (you may get heat or a/c in this config - does not matter)

    If all this works look at a new thermostat. Please update on your progress and success. Thanks

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Carrier Heat Pump we turned it to heat, inside fan runs outside fan doesn't [ 1 Answers ]

We changed our heat pump from AC to heat, noticed the inside fan ran all night. Checked in the morning and the outside fan wasn't running. Turned it off and back on there is a click but the fan doesn't start. Turned the setting back to AC to see if it would run acts the same as with heat, exterior...

My Carrier heat pump will not shut off. [ 1 Answers ]

I've had a couple problems with the unit not coming on or going off before. I have taken sandpaper and cleaned the contacts when it would'nt turn on before and it seemed to run fine for a couple days. Right now it will not turn off and after looking through some of the troubleshooting questions and...

Fan on carrier thermostat won't shut off [ 1 Answers ]

Model 25 HBA The light on my thermostat went out and the fan keeps blowing. There seems to be two breakers for the furnace that I will be checking. What could be causing this malfunction. Thanks... Kathy

Carrier Fan won't shut off [ 4 Answers ]

Having an issue that just started recently with our Carrier 58GP Series 100 furnace. At first it had the symptoms of a bad limit switch, furnace would turn off, blower off, then blower back on and off. I didn't replace the limit but am now having a different problem, the blower won't shut off...

Carrier gas furnace fan won't shut off [ 23 Answers ]

We have a 21 yr. old Carrier gas furnace and I just changed the air filters. When I put the cover back on, even though the thermostat was turned to off, the fan started. I even disconnected the thermostat, but the fan kept going. It runs 24/7. When I finally turned the thermostat to "auto",...