    Split-bus ITE panel help
    Have an existing service to 1200 SF 3br/2bath 1975 residence:

    ITE Model EQC5X12B 120/240 200A with 60A split, no main feed breaker.

    I know this type of panel is out of date/code, however, can't spend the money right now. There are 6 tandem slots one of which is the 60A breaker for the lower bus. This home once had baseboard heat (now converted to natural gas) that utilized two 20A tandem slots above. In the remaining three tandems are; the range (40A), dryer (30A) and water heater (30A).

    I planned to utilize the two abandoned baseboard slots for:

    Bus 1
    20A ref
    15A furnace
    Bus2
    20A garage (should I ever need freezer)
    15A smoke detectors

    Does anyone have comments on this application other than "replace this panel?"

    Thanks very much for your input!
    hfcarson's Avatar
    hfcarson Posts: 1,003, Reputation: 49
    Ultra Member
     
    #2

    Feb 3, 2012, 01:25 PM
    OSUChE,
    Out of date, yes likely...
    Although, many states in the US have "rehabilitation" sub-codes or similar documents which may not require you to replace an existing service / panel...

    If I understand what you're describing, your panel has (6) two-pole breakers in the top half that if you shut off will turn off the entire panel? If so, then the panel is still code compliant. It's called the six switch rule and it's maximum number of switches allowed to completely de-energize the service.

    That may be more than needed, sorry I digress...

    Anyway you propose to use the (4) slots that have been opened up when the baseboard heat was removed?
    Doing this will increase the maximum number of operations to turn off the panel to (8). That would be a code violation. Why not consider a small, say 60 ampere sub-panel? It will keep you code compliant and will give you additional space for other things you haven't yet discovered!

    But always.. be safe

    OSUChE's Avatar
    OSUChE Posts: 2, Reputation: 1
    New Member
     
    #3

    Feb 3, 2012, 03:26 PM
    @hfcarson:

    Yes, I believe you're correct, and that would make 8 operations. Would it be compliant to two-pole the 15A and 20A? I'm guessing no since they serve different circuits?

    If not, I will go with your suggestion and hit Home Depot up for a sub. Thanks for helping!

    And indeed safe, safe, safe! I'm a chemical engineer with a Pulp Mill background in addition to all those G/C years. I understand the consequences of short-cutting safety around live line volt/amps! Thank you for mentioning it, easy to be complacent at home for certain! ;)

    Rick

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

No neutral bus in FP electric panel, what can I do? [ 4 Answers ]

I do know I need to upgrade the box but I need to install my electric dryer immediately for use. I have the breaker ready to install but have come across the problem of I see no neutral bus bar for the neutral wire. What can I do or can I install a bar on my own?

Can I add another neutral bus-bar to aservice panel? [ 1 Answers ]

I have more circuits that I can add onto my service panel but have run out of neutral slots on the bus-bar what can I do?

"EQ" Load Center catalog # EQ4X16A (ITE Panel) [ 45 Answers ]

To all, My current "Honey Do" is to upgrade from AL to CU cabling. I hit a wall when I pulled the main panel door. Attached is a picture of the installed panel. All labels are eaten or scratched/rotted away. I believe that Noah had installed a similar panel on his Arc before the rain storm. ...

Adding a bus to a main panel for ground. [ 2 Answers ]

I have recently added on a room to my house. I have a main power supply out side with a two pole 100 amp breaker the neutral and ground are on same bus, the ground continues down tocopper pole in ground. Upstream ihave added alager box to accommodate more poles. The new box has the two hot wires...

Adding a nuetral bus to an old main panel [ 5 Answers ]

Greetings... Can I add a neutral bus to my houses main panel... I have one bus in there now that is for both nuetral and ground... when I go to hookup the neutral from my 220 gfci breaker to that bus I keep tripping the breaker... the spa is a 3 wire 2 hots and a ground... the instructions say to...


View more questions Search