    Minimizing Voltage Drop in a 50 foot outdoor run
    I have a 50 foot run from my breaker panel to my garage where I will put a junction box to distribute the power to a light, 2 outlets and a garage door opener.

    Currently there is a wire already suspended from the mast head to the garage, and I plan on hanging my wire from that.

    I know there will be a voltage drop but I'm not sure how much. It's going to be on a 20 amp break so I was thinking a #10 UF would prevent voltage drop for that kind of distance. What do you guys/girls think?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #2

    Feb 2, 2012, 01:32 PM
    I think for 50' it is not worth worrying about.
    #12 is fine.
    CliffARobinson's Avatar
    CliffARobinson Posts: 1,416, Reputation: 101
    Ultra Member
     
    #3

    Feb 2, 2012, 01:34 PM
    Calculating Voltage Drop - 1 Phase

    I (Amperage - also known as Current)

    VD (Voltage Drop)

    R (Resistivity of wire - taken from NEC Chapter 9 Table 8)

    L (Length of run - we typically calculate the drop per 1000 ft lengths)

    CM (Circular Mils of Wire - measure of the diameter (thickness) of the wire - again available from NEC tables)

    K (Resistivity Constant - 12 for Copper, 18 for Aluminum)
    Source: Electrician-ElectricalContractor.com
    UsaveU's Avatar
    UsaveU Posts: 25, Reputation: 1
    New Member
     
    #4

    Feb 2, 2012, 01:39 PM
    Thanks, that makes my wallet happy.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #5

    Feb 3, 2012, 09:38 AM
    Not really, you cannot use type "UF"(Underground Feeder)for an above ground run if is not listed for that usage. If it is, you should see, "Sun light Ristance" or similar words on the cable sheath.
    ballengerb1's Avatar
    ballengerb1 Posts: 27,378, Reputation: 2280
    Home Repair & Remodeling Expert
     
    #6

    Feb 3, 2012, 09:42 AM
    Once again Don is correct.
    UsaveU's Avatar
    UsaveU Posts: 25, Reputation: 1
    New Member
     
    #7

    Feb 3, 2012, 10:05 AM
    What kind should I use?
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #8

    Feb 3, 2012, 10:09 AM
    UF cable is rated sunlight resistant.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Voltage drop [ 2 Answers ]

I have to feed a pump it has a load of 30 amps, is 115 volts and is located 1300 feet.

Voltage drop [ 4 Answers ]

If i have a 3 phase motor running in 440volts and drives the cetrifugal fan, then the voltage drops to 20 percent, what happened to running current does it increas or decrease.

Voltage Drop [ 3 Answers ]

I am trying to illuminate a tunnel about 3000' long temporarily with 9- 400 Watt Metal Halide fixtures spaced about 320' apart. I have a 120/240 generator single phase that I will use to back feed a 240/480 volt transformer to deliver 480 volts, single phase to the tunnel lights. At 480 volts I...

Voltage drop [ 4 Answers ]

A 300sq mm cable is to be laid for 600mtr. Distance. As the distance is large so there are considerable voltage drop at the receiving side. How can we cope up with this voltage drop at the receiving end? We want a constant voltage ofd 415 V at receiving end irrespective of input voltage? ...

Voltage Drop [ 2 Answers ]

I have a 20 amp breaker;there are a total of 7 receptacles on this circuit with a 15 amp GFI on the first receptacle. The first 5 receptacles in line work fine, the last two receptacles which are approximately 70 feet from the 5th receptacle flip the 15 amp GFI off when plugging in a drill. I...


View more questions Search