    Bryant gas furnace thermostat wiring?
    I have an older Bryant Funance 80 system with A/C. The other day, the furnace would not ignite electronically. It was deemed by the serviceman to install a new board. So the new board was installed and the ignitor works but the furnace is short cycling.. meaning the burner comes on for just a few seconds and then shuts off and then cycles again.

    Then the serviceman says I probably need a new thermostat. The thermostat I had was a Honeywell that was non-programmable and has separate controls for Heating and A/C plus Auto and On for the fan. The serviceman said I could put a jumper wire on the Rh and W contacts and the heat would work but never shutoff until I unhooked the jumper.

    I went out and bought another Honeywell thermostat to match so that I could easlity replace the existing one. Prior to me installing the new one, I would like to know a few things. On the Bryant circuit board, the following 5 wires are used and attached to the thermostat termainal blocks which has the G, C, W, why, and are terminals.

    My first question is why do I have to jump between the Rh/Rc and W contacts on the thermostat to makue the funace burner to continuously run?
    The second question is why is there a jumper between the G and why terminals on the circuit board, instead of just having the G go to G on the thermostat and why going to why on the thermostat?
    davmou's Avatar
    davmou Posts: 3, Reputation: 1
    New Member
     
    #2

    Dec 9, 2011, 10:59 AM
    Went and checked the wiring, there are 6 wires on the circuit board thermostat terminal block... red on G, white on Y, red on Y, white on C, white on W, and red on R. I did find that one white wire had snapped off so I trimmed and reattached it. Of those 6, only 4 go to the honeywell thermostat and of them, red is on Rh with jumper to Rc, white is on W, white is on Y, red is on G. And the other 2 go to the outdoor A/C unit. With that configuration, the unit fires the burners for a few second and then is extingushed and then recycles and does the same thing.
    davmou's Avatar
    davmou Posts: 3, Reputation: 1
    New Member
     
    #3

    Dec 9, 2011, 11:46 AM
    I installed the new thermostat and everyhting is working fine... thanks

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Bryant Model tstatbbpb501 Thermostat Wiring [ 0 Answers ]

I moved into a rental home and the thermostat is operating erratically. When the system is set to Off, the fan runs. When the system is set to heat, it works fine until it's up to temp then cold air continues to blow through the house. I looked at the thermostat wiring and Red is to R. Green is to...

Weil-mclain gas furnace thermostat wiring? [ 0 Answers ]

How to install a thermostat in weil mclaing gas g boiler it show that there are Y G W C R in the transformer at the present time I don't have a thermostat connected is working with a timer and I would like to install a thermostat There wires connected to the C , G, R I FOLLOW THE TWO WIRE THAT...

Thermostat to Gas Furnace basic wiring. [ 2 Answers ]

I am missing one of the wires that goes from the thermostat to the furnace. I can't find the other one but can you tell me where it should go. I have a very old oil burner that has been converted to gas. If you can point me in the right direction I could probably figure it out. Thank you ...

Add AC to old gas furnace thermostat wiring [ 2 Answers ]

Hi. I am adding AC to an older furnace and I can't figure out how to wire the 24V Thermostat wires. I only see three places to hook wires in, labeled: TH, TH-TR, TR. Each terminal has two places to hook in wires. Right now, it is wired for heat and works perfectly with two wires coming from the...

Thermostat air conditioner wiring for tempstar gas furnace [ 2 Answers ]

I disconnected my thermostat from the gas tempstar furnace and also disconnected two wires I traced to the central air conditioner. I do not know where to connect the air conditioner black and white wires to on the W,Y,R,G,C. I do not have a manual. Can someone help me?


View more questions Search