    Scott999's Avatar
    Scott999 Posts: 2, Reputation: 1
    New Member
     
    #1

    Nov 22, 2011, 10:50 AM
    Three Wire Aerial Feed to 100 amp subpanel
    I am hooking up a 100 amp subpanel with a 2/2/2 overhead wire. Is the overhead bare wire a neutral or a ground? Should I take the connector bar out that is pre-installed in the subpanel between the neutral and ground bars? Should I bond the panel with the bonding screw? (I am backfeeding the sub to a 100amp brkr so I have a service disconnect.
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Nov 22, 2011, 11:35 AM
    Are you located in the U.S.A.

    If you are, then you need to understand some basic information.

    To begin with, Neutral and Ground serve two distinct missions.

    Neutral is the return path from the source to the circuit terminus.

    How far is the distance between the source (main panelboard?) and the location of the secondary panelboard?

    A secondary panel feeder, must be 4 wire. 2 (hots), Neutral, Ground.

    There are mast heights and locations that need to be reviewed by you. I'm pretty sure that you will be required to get a permit.

    At the secondary location, the panelboard can be either a MCB or a MLO panelboard.

    If I were doing the work, I would set an Emergency Cut Off switch in front of a MLO panelboard.

    At the secondary panelboard, Neutral and Ground must be isolated from each other. That means that you must use a separate Grounding System.

    Neutral and Ground conductors cannot be put on the same bus
    Bar. Neutral and Ground cannot be bonded to each other anywhere else but at the Main Panel board.

    Just curious but did you do a load calculation at the new location to make sure you actually need 100 Amps?
    Scott999's Avatar
    Scott999 Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 22, 2011, 02:35 PM
    Yes, here is a little more info, thanks. It is USA, This panel is actually the second subpanel. The first one is a 125 amp 4 wire underground fed subpanel. I am adding a second subpanel fed from the first. Coming out of the first I have a disconnect breaker (100 amp), I have 2/2/2 going up the mast to the arial wire which is a 2/2/2 arial wire connected with split bolt splices rubber and taped. The overhead wire is only three wire as described two sheathed and 1 bare. When I get to second mast split bolt to three sheathed #2 wires running down the mast to the second panel. Both leads feed another brkr. For disconnect. The third wire is connected to the neutral bar. At this time the neutral and the ground are connected by a copper rod. I don't know if the panel is bonded by the bonding screw. There is a number 4 bare to a ground rod attached to the ground bar. My issue is that we are noticing some surging from the equipment operation. I checked at the first panel and have 246v, and each leg is showing about 114v. At the second although I have 248 volt reading both legs together. When I measure each one I get 148 volt on one leg and 97 volt on the other. There in lies my problem. What and why do you think that is? Thank you for your time and consideration on this. It is appreciated.




    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #4

    Nov 22, 2011, 03:31 PM
    The bare neutral conductor has a loose connection and needs to be repaired immediately. Or can be anywhere in the neutral circuit.

    Shut power off to the sub panel as the abnormal voltages can damage equipment, and at times has caused fires.

    I do not have time with the details of your installation right now, someone will get back you.

    Get the wiring repaired ASAP.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Overhead from a 100 amp service panel to a 100 amp subpanel in a garage. [ 6 Answers ]

An Electrician friend said I could use #4 copper for the (2)120 volt legs and a conventional Suspension wire as the nuetral. The overhead span is about 35 feet and the overall run From panel to panel is about 70 feet.The supply outlet said to use #2 copper. Also, what type wire for sunlight...

100 amp main, 100 amp service wire, 200 amp sub panel? [ 2 Answers ]

I am moving my sub panel and upgrading to a 200 amp service, but in phases. The first phase is to move the panel due to some remodeling. I want to put a 200 amp panel in the laundry room with a 200 amp breaker. I have 100 amp feeder wire going to it (AL 2/2/2). Outside I have the meter can and...

3-wire feed to subpanel in shed - bonding and grounding? [ 4 Answers ]

I have a 240 volt, 3-wire, 10 gauge feed from my house to a subpanel in a remote shed that has been there for at least 20 years. This feed is protected by a 30amp breaker on the house panel. There are no other metallic connections between the shed and the house The subpanel in the remote shed...

How many conductors to wire a 100 amp main breaker subpanel in detached garage. [ 3 Answers ]

How many conductors do you have to run to a main breaker subpanel which is located in a garage 100 ft away. Can you get away with 2 hots and a neutral If you pound a ground rod at the subpanel. I cannot find the answer in the code book.

Can I run a 50 amp subpanel if a 100 amp main if so what size wire [ 1 Answers ]

Can I run a 50 amp subpanel from a 100 amp main and if so what size wire


View more questions Search