    How do I test a suspected short in a White Rogers 36E gas valve for a Carrier furnace
    I have a carrier furnace with a White Rogers 36e gas valve. When I measure Resistance between terminal #1 and Ground I get 0. When the bimetal at the pilot connects 24VAC to the terminal it pops the fuse on the control board. I think the valve is bad with a short. How should I be testing this. Terminal 1 to Gnd?
    T-Top's Avatar
    T-Top Posts: 1,871, Reputation: 100
    Ultra Member
     
    #2

    Nov 18, 2011, 07:02 PM
    The good Ole 5 wire gas valve not very service friendly. Give the make and model of your furnace will help. It's a pilot,pick and hold gas valve. Give as much info as you can about your system a short can be anywhere
    draflynn's Avatar
    draflynn Posts: 3, Reputation: 1
    New Member
     
    #3

    Nov 19, 2011, 08:28 AM
    Thanks T-Top. The unit is a Carrier 58ssb deluxe upflow gas furnace (cir 1985?). Spark pilot with a 3 wire bimetal. The bimetal is working. Both sides, NC and NO. The inducer is working. The air flow diaphram/switch is working, NC and NO sides. More detail about the problem - > I found the unit with the fan running all the time. The pilot was cycling but no main gas. I removed the control board and found a burned run on the back. Turns out to be the 24v ckt that pulls the NC heat fan relay open to turn fan off. I repaired the run. Simillar behavior but now when the main gas solenoid gets power (Terminal #1), it pulls the 24v ckt to 0 and the unit shuts down momentarily. It killed the control board fuse on the second cycle. Now I remove the wire from terminal 1 on the valve (main gas), The furnace cycles as it normally should. The fuse does not blow. Check resistance from valve terminal 1 and find 0 ohms, short. I found some reference to other valves that should measure 50 to 80 ohms. I think I need a valve. Thanks Again!
    draflynn's Avatar
    draflynn Posts: 3, Reputation: 1
    New Member
     
    #4

    Nov 19, 2011, 08:33 AM
    One other big detail. I did replace the board after the run repair. The fuse that was blowing is on the new board. The old board did not have a fuse. So between "unit shuts down momentarily.( add replaced control board) It killed the control board fuse"

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

How to test a White Rogers 2 stage gas valve? [ 19 Answers ]

Hi, I have a Magic Chef Furnace with a Robertshaw Ignition Module and White Rogers Gas valve. The problem is that the gas valve will not open to start to flame to the furnace. If you turn up thermostat, I then get spark and then a pilot light. Then nothing. I have replaced the Ignition Module and...

I need a user's manual for a white rogers heater 36E [ 3 Answers ]

How do I get a user's manual for a White Rogers furnace #36E? David Bale 775-626-3018 [email protected] Thank you

White Rodgers gas valve 36e troubleshooting [ 3 Answers ]

I have a Lennox G23 furnace with a White-Rodgers 36E24-204 NG valve that continually is tripping the limit switch, due to a condition where the pilot is putting out way too much flame. I can see areas on the plate where the limit / rollout switch sits, and the flame has deposited large amounts of...

Carrier Natural Gas Furnace main gas valve will not open every call for heat [ 1 Answers ]

We have a Carrier Weather Maker 8000 Natural Gas Furnace not functioning properly. We have replaced pressure switch, hot surface ignitor, flame sensor and control board. It will cycle 3 to 4 times and then not come back on. Is it possibly a bad coil on gas valve?:rolleyes:

White-Rogers gas valve [ 7 Answers ]

Hi all, I'm new here, so bear with me, please! I have a Weil-McLain boiler (M#-CG-8-SPDN, 245,000 BTU) that I use to heat my home. I attempted to start it last week, but the pilot light was out. I tried to re-light it, to no avail. I removed and 'shined up' the thermocouple, but that did no...


View more questions Search