    Main Panel to Sub Panel wiring
    The feeder cable for a 30A to 40A subpanel is supposed to have 4 conductors? 2 live, 1 neutral, 1 ground. Correct?

    I have a Cutler 200A main panel. What kind of a "feeder breaker" would I use to be able to drive 2 live wires in this cable?
    Thanks very much!
    donf's Avatar
    donf Posts: 5,679, Reputation: 582
    Printers & Electronics Expert
     
    #2

    Nov 15, 2011, 05:34 PM
    The description of the conductors in the cable is correct. What you also need to know is the amperage the cable is to carry. If the distance is over 100 ft. then you should also consider the voltage drop. The total end to end voltage drop cannot exceed 5%.

    If you want to carry 30 Amps then you need 10/3 cable.

    If you are going to use 40 amps, then you will need to use a #8/3 cable.
    fw_man's Avatar
    fw_man Posts: 2, Reputation: 1
    New Member
     
    #3

    Nov 15, 2011, 07:50 PM
    I will be going 2 feet at most. So I will use either a 10/3 or an 8/3 cable. What about my second question:
    I have a Cutler 200A main panel. What kind of a "feeder breaker" would I use to be able to drive 2 live wires in this cable?
    stanfortyman's Avatar
    stanfortyman Posts: 5,598, Reputation: 279
    Electrical & Lighting Expert
     
    #4

    Nov 15, 2011, 09:22 PM
    Quote Originally Posted by fw_man View Post
    I will be going 2 feet at most. So I will use either a 10/3 or an 8/3 cable. What about my second question:
    I have a Cutler 200A main panel. What kind of a "feeder breaker" would I use to be able to drive 2 live wires in this cable?
    Either a 2-pole 30A or a 2-pole 40A, depending on which cable you use.
    Make sure it matches the panel type. Mainly Cutler has CH and BR style breakers.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Sub panel load size from main panel 200 amp to 100sub 350 ft [ 1 Answers ]

Wire conduit size fromm a main 200 amp panel to a 100 amp sub panel 350 ft away

Wiring a sub panel of the main panel. [ 3 Answers ]

Hello I am looking for some guidance regarding wiring a sub panel into my porch. My home is close to 40 years old and never had heating or plumbing. I recently had to build a porch to allow for these upgrades. This sub panel is to accommodate an electric hot water heater, water pump outside plug...

Main to Sub Panel Wiring [ 3 Answers ]

I received an answer prior to wiring this up, but am a bit confused. I think I was told to keep the ground separate at the sub panel but am not sure. If so, I only need to pull 3 wires (2 hot legs and 1 neutral). I have attached my PDF for your review. Thanks, ...


View more questions Search