I am replacing the floor in an upstairs bathroom.
Can I put the P traps for the bath and shower 3 metres away (after a bend) outside where we can get to them for servicing if ever we need to? Instead of directly beneath them where we can never maintain them if they leak or need servicing.
Thanks
Bruce
|
|
 |
Senior Plumbing Expert
|
|
Oct 26, 2011, 04:13 PM
|
|
Hi Bruce...
Good question. I am afraid, however, that by moving the PTRAPS away from directly under the fixtures you will effectively be creating STRAPS and these are illegal and can cause the traps to siphon and allow sewer gasses to enter the home... a definite no-no. Never mind that once you open the floor up you may even find some vent connections that must go after the ptrap (closer to drain) and moving the PTRAPS would certainly be a problem in that case, too!
Keep in mind that if you ever need to service the 2" shower PTRAP you can easily snake the drain (such a large pipe) and you can also use a wet vacuum to clear the ptrap real good if needed... ;)
The tub trap can be made accessible via an access panel and if the vent is above the floor you can install a full size test tee cleanout in the vent at just above the flood level rim of the tub and snake through this cleanout if the tub ever clogs up!
Any more questions just let me know, OK?
Mark
|
|
 |
Junior Member
|
|
Oct 26, 2011, 11:49 PM
|
|
Everywhere I know of running traps are illegal, the only exception I know of is in a outside overhang where the trap could freeze.
|
|
 |
New Member
|
|
Oct 26, 2011, 11:56 PM
|
|
Thanks Mark, but does it still create an "S" trap if the 3 metre pipe going outside is followed by a "p" trap then a vent before it goes down to ground.
|
|
 |
Senior Plumbing Expert
|
|
Oct 27, 2011, 05:19 AM
|
|
Yes it does... still creates an ILLEGAL RUNNING TRAP... see image. These traps are illegal because they have a tendency to get siphoned via "capillary action" and allow sewer gasses into the home. I recommend that you stay with code... ;)
Why the concern here? Have you had a few bad experiences with ptraps and getting to them?
Are you replacing the pipes? If so, then you shouldn't have to worry about trap issues for years/decades!
Back to you..
|
|
 |
Eternal Plumber
|
|
Oct 27, 2011, 08:15 AM
|
|
What nobody's touched on is the 10 foot line from the drain to the trap. You will have 10' of rotting hair and rancid grease to smell out of the drain, Traps are there to prevent that. Install the trap under the drain and stay odor free and within code. Good luck, Tom
|
|
 |
New Member
|
|
Oct 27, 2011, 10:26 PM
|
|
Thanks guys you have all been very helpful I am taking no chances the P traps have been fitted under the shower as you all suggested and up to code. Regards Bruce
|
|
Question Tools |
Search this Question |
|
|
Add your answer here.
Check out some similar questions!
Maximum trap distance?
[ 6 Answers ]
Is there a maximum horizontal distance that a trap can be from the drain?
I have a mid-60s bi-level house that has a cantilever on the upper section. As shown in diagram #1, the original shower base extended over the cantilever and the trap was right under it. I gutted the bathroom and...
Maximum distance from tub to trap
[ 7 Answers ]
In order to provide a convenient place to locate a drum trap for a bathtub, and in order to meet the 5' minimum distance requirement (from trap to vent), I will need to place this trap about 6' from the actual tub drain. Is this acceptable, or is there also a maximum distance requirement that must...
Maximum distance from sink to p trap
[ 5 Answers ]
Hi,
What should the maximum distance be from the bottom of the sink to the p trap. If I stay within this distance is there any problem installing a p trap below floor level? I want to do this because of space limitations when installing a pedestal type sink.
Thanks,
Tom
Distance for p-trap above floor and to first tee
[ 4 Answers ]
Hi All,
I'm a new home owner (or should I say owner of a really old pre-owned house). I'm looking to add a washing machine on the second floor in my pantry. I installed the dryer vent, the electrical, and have the rough plumbing pipes running down into the basement ( only the hot/cold water is...
Vertical distance to trap
[ 3 Answers ]
I'm installing a basement shower. When the house was built 2 years ago, it was pre-roughed, with a plastic cover over the hole where the drain will be. I was surprised after opening up and removing some dirt that the 2" horizontal drain line is so deep - it is 12-1/4 inches from the top of the...
View more questions
Search
|