    Gas furnace cuts off
    I have a carrier gas furnace. It starts fine. That is, the inducer motor starts, the igniter glows, the gas comes on and lights, igniter goes off, the air handler starts. Runs for anywhere from 15 to 30 minutes. Even cycles a few times if house reaches thermostat setting. But eventually, always within 1 hour, it always shuts down and has blinking lights. I can shut power off and reset it or it will reset itself after 3 hours and repeat process. Any help?
    louisn's Avatar
    louisn Posts: 2, Reputation: 1
    New Member
     
    #2

    Oct 19, 2011, 07:18 PM
    Count the times the light on your mother board shows a long light will be a 1,2,3, a fast light will then be the other number. Your panel will tell you what the problem is
    JonesHVAC's Avatar
    JonesHVAC Posts: 173, Reputation: 12
    Junior Member
     
    #3

    Oct 20, 2011, 05:19 AM
    If you cannot find this, post the model number and we will do our best to help you.
    Roberts1987's Avatar
    Roberts1987 Posts: 2, Reputation: 1
    New Member
     
    #4

    Oct 20, 2011, 05:58 AM
    The code is 14. Maybe I can give a little more info I got after watching it a little closer. Once the system has shut down and the code 14 is blinking and the system is completely cooled down, If I reset it by shutting off the power, the unit will start and work normally the first cycle. When I watched, the house had cooled to 65 degrees. The thermostat was set on 69. The unit fired up and ran fine until the house reached 69 and the turned off normally. When the dropped back to 68, the inducer came on, the igniter glowed, the gas came on and lit for a few seconds and then shut off. This repeated 3 more times I think then the code started flashing. Thanks, John.
    JonesHVAC's Avatar
    JonesHVAC Posts: 173, Reputation: 12
    Junior Member
     
    #5

    Oct 20, 2011, 06:15 AM
    I'm leaning toward a bad stat... remove it and jumper the red and white wire let it run for 15 minutes and then remove the jumper and let it cool down so it completely stops and then jumper it out again after a couple minutes. Let it run for another 15 minutes and repeat two or three times. If the furnace operates properly then replace the stat, if not post back and we will look into other things.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Gas Fireplace cuts out for no apparent reason [ 2 Answers ]

I have a gas fireplace manufactured by Superior. It is model DS-36TN. The unit was in the house when I bought the place in 2002 and worked fine for the past several years. About 2 months ago it started cutting out after being on for anywhere between 20 min and 1 1/2 hrs. I always turn the...

My GE gas dryer cuts out in the middle of cycles [ 1 Answers ]

Y GE gas dryer cuts out in the middle of cycles when hooked up the external vents, it takes afew minutes break and then restarts, when I unhook itfrom the exteriorvent it does a lot better, the vent has been cleaned so I donth think there is a blockage issue, the dryer is about 8 years old, that...

Furnace cuts in and out [ 0 Answers ]

fuel oil furnace cuts in and out during the pump running at random times. Fuel is 8months old approx. It started doing it at the end of me using it this past spring and is still doing it now that I'm starting to use it again filter is about 1 year old and the furnace worked fine for quite a while...

22hp briggs cuts off/runs out of gas when hot [ 3 Answers ]

The mower slows down and runs out of gas when it gets hot at times. Let it set for a few minutes to cool off and it will start back. Gas filter is empty when it cuts off, and will fill back by itself when it sets for 10 to 15 min. any suggestions! Thanks


View more questions Search