    I have 2 outside AC units for diff zones and all of a sudden neither kick on??
    2 outside ac units for diff zones in the house and seems all of a sudden neither is getting signal or power to turn on to condense cold air? Checked breakers but not the outside ones as they looked OK?/?? Any sugg's
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #2

    Sep 8, 2011, 06:04 PM
    I would check your Breakers, that should be the only thing common with both, if 2 units.
    If 1 unit an 2 zones it may be different, can you confirm which?
    Do you have 2 thermostats?
    hklimovi's Avatar
    hklimovi Posts: 3, Reputation: 1
    New Member
     
    #3

    Sep 8, 2011, 06:11 PM
    Yes --- 2 Zones / 2 Units, fans in attic kick on but outside units no! Thermostat batt's changed and fresh. Each unit is on their own direct line to the breaker box. There are outside breakers that are the cylender type but why would they both go at the same time?
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #4

    Sep 8, 2011, 06:18 PM
    I would check:
    Both inside breakers disconnects are On/reset, both outside breakers are on/reset, verify voltage out of the 4 disconnects have power out.
    Only other way I could think affecting both is if recent remodeling/construction severed both control wiring of both units.
    Does the inside blower work?
    I believe you have 2 units.
    2 zones are usually 1 unit?
    hklimovi's Avatar
    hklimovi Posts: 3, Reputation: 1
    New Member
     
    #5

    Sep 8, 2011, 06:27 PM
    2 blowers in attic /// 2 units outside. Yes blowers (for both work), outside condensors do not kick on. Mind you the thermostat wires from attic to outside units run from attic through ( I think) soffit down a downspout to the (2) units (seperately).
    Stratmando's Avatar
    Stratmando Posts: 11,188, Reputation: 508
    Uber Member
     
    #6

    Sep 8, 2011, 07:00 PM
    Do you have voltage out of outside disconnects?
    Then , do you have 24 volts at outside compressor contactor coils, If so, do they energize and put 240 volts out of load side of contactor?
    If 24 volts is present, thermostat is sending voltage and control wiring is good.

    2 Questions:

    Do you have 240 volts out of contactor/out of disconnect?
    And
    Do you have 24 volts present at contactor coil when thermostat is set to cool?

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Kick baby kick [ 5 Answers ]

This is my first pregnancy and I'm 18 1/2 weeks and I felt my baby kick couple of times and now he hasn't kicked and a few days and rite now its about 1:45am so obgyn is closed but should I be worried

1 Unit, 2 zones and a damper [ 4 Answers ]

What are your thoughts on a single AC setup with a damper systems with 2 zones? What are your thoughts on dampers? Please reply ASAP. Rob

Crossing time zones [ 3 Answers ]

If if fly from east to west and cross time zones the time will change say from 2am to 1 am to midnight. It would seem as though I should run into yesterday but instead I run into tomorrow. How come?


View more questions Search