    My heat pump on my goodmen,when I put the a/c on it blows hot
    What would it be
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #2

    Aug 23, 2011, 06:00 AM
    Your reversing valve is not pulling in for some reason. It could be stuck or may not be getting power (24 volts). It could be anything from a broken orange wire ("O") or a bad t-stat. You will have to use a meter to trace it out and find out why it is not working. DrTom4444
    larbear1's Avatar
    larbear1 Posts: 4, Reputation: 1
    New Member
     
    #3

    Aug 23, 2011, 06:13 PM
    It is a new t-stat,I will test the orange wire, thank you
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #4

    Aug 23, 2011, 06:23 PM
    If you wired it wrong when you put in the new stat you have your answer. Some heat pumps use the "B" terminal and others use the "O" terminal and use either a blue or orange wire. When the heat pump needs "O" for cool then the "O" terminal is used while others use the "B" for heat. You probably have the "O" type as they are more common. DrTom4444
    larbear1's Avatar
    larbear1 Posts: 4, Reputation: 1
    New Member
     
    #5

    Aug 23, 2011, 06:47 PM
    I put in a h-well pro5000, red-rc, yellow-y, blue-c, brown-o/b, green-g, white-aux
    larbear1's Avatar
    larbear1 Posts: 4, Reputation: 1
    New Member
     
    #6

    Aug 23, 2011, 07:18 PM
    I put in a h-well, red-rc jump r,yellow-y,blue-c,brown-o/b,green-g,white-aux
    drtom4444's Avatar
    drtom4444 Posts: 3,282, Reputation: 145
    Ultra Member
     
    #7

    Aug 23, 2011, 08:53 PM
    When you put it on cool you need to check between C (common) and "O" and see if you have 24-30 volts. Make sure the brown goes to the "O" terminal out on the condensing unit. The "Y" just pulls in the contactor and the "O" decides whether it is in heat or cool cycle. Some heat pumps are wired with "B" instead of "O". You can turn off power to outside unit and when power is put to "O" you will hear a click if it is working. There is a solenoid on reversing valve so you need to see where the two wires from the solenoid go and test the voltage there where it should read 24-30 volts when calling for cooling. If not you have something wired wrong. DrTom4444

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Heat pump never turns on, handler blows continuous with no heat except with AUX heat [ 2 Answers ]

10 year old Rheem air handler RHBA-21J8MFCA, 1/3HP, 2.8A. New WeSt Columbia, SC 29170, Model 2HP13L48P-1B, HCFC-22, 4TON. Installed new out of box iN July and AC working splendidly but start-up is "violent" and loud. Installer says I need some sort of "start-up kit". I put off as had planned...

Goodman heat pump does not switch on for heat and the AC blows A/H fuses. [ 4 Answers ]

My Goodman heat pump, model GSH130361AD, heat does not switch on (outer unit). When it first went out, the Honeywell T8411R t-stat digital display went blank. First, I tried replacing the stat with other, but they only accommodated 5 wires. Wiring to the Honeywell was 7 wires. I'll come back to...

Heat Pump blows 5amp fuse when switching between defrost & back to heat. Them Heat work [ 3 Answers ]

I have a Carrier Heat Pump System. It’s about 5 years old and has functioned OK until this Christmas Eve. One problem is the condensing unit is not kicking back on after it goes into defrost mode. I found a 5AMP fuse blown in the attic unit and once replaced it functioned. At least for a day or two...

20 yr old Lennox heat pump fan blows constantly in heat mode [ 5 Answers ]

20 year old Lennox heat pump - outside temps been 30's at night, 40's daytime UPDATE: I went outside and the unit is covered in frost on 3 sides! I've been reading on Google about frosted heat pump units and can't determine how to manually defrost it. Apparently, the auto defrost is not...

Heat Pump Thermostat Set to Cool, Blows Hot Air [ 6 Answers ]

Having a problem with my heat pump system. The thermostat is set to cool but the unit is blowing hot air. If it has been turned off for awhile and we turn it back on to cool (fan set to auto), it will blow at what seems to be room temperature for awhile (5-20 minutes) and then turns to hot air...


View more questions Search