    What size underground cable do I need
    I have a 175' run from panel to an outlet for a swimming pool pump that says 10 amp on it. What size cable do I need to use to make that run.
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #2

    Jul 25, 2011, 11:43 AM
    Assuming 240 volts, which is a value needed to do voltage drop calculations, I would use #10 copper wire.

    One problem with your plan, cable is not allowed for pool wiring.

    You can use 3/4" PVC conduit, buried 18 inch deep, and pull three #10 THHN/THWN conductors.

    There are other requirements for pool wiring, ground fault protection of the pool pump circuit, 120 volt outlet required nearby, grounding, etc. You need to consult with your local inspector to learn what their requirements are for these issues.

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Cable size 120 mm2 with matching lug size [ 5 Answers ]

Cable size 120 mm2 with matching lug size

Patching 2-2-2-4 underground service cable [ 6 Answers ]

This is about a 200' run to a workshop/office. It was nicked during excavation several years ago and subsequently developed a break (water penetrated the patch and turned the aluminum to powder). At that time, I dug up the cable, and had a local electrician splice with some epoxy type connector,...

Generator underground feed cable size [ 18 Answers ]

I need to install a 175 foot underground feed between a generator and a building and need help with finding the wire. My research indicates I can use either a copper 2-2-2-4 thhn or aluminum 00-00-00-1 thhn in a grey schedule 40 conduit. Is my research correct? What is the precise desingation...

Grounding cable depth when ran underground [ 2 Answers ]

I am upgrading from a 100AMP to 200AMP service. I need to run a grounding wire (bare CU #4AWG) from 2 grounding rods to the main electrical panel: 50 feet. I plan on running it underground. I wonder whether the minimum depth of 24" (18" if in PVC conduit) applies to grounding wire installed...

Underground wiring, electrical, cable, telephon [ 2 Answers ]

We are replacing an underground electrical wire that shorted out which supplies power to our pool filter and pool house. In this same trench (18" deep and 175ft long) we would like to put a telephone and a cable line for TV and phone by the pool. Any problem putting these in the same trench?


View more questions Search