    Installing subpanel in basement
    I would like to install a subpanel in my basement and will need a lot of advice.

    Overview:

    We have 100 amp service delivered to an outside meter and box with a 100 amp breaker. There is a copper cable from the box attached to a buried ground rod. A Romex-type cable goes from this box (3 wires plus ground) through our garage attic to the main panel in the mudroom (about a 30 foot run). There is a 100 amp main breaker in this panel, but all of the other circuits are 15 amps. I would like to bring (approximately) 100 amp service into the basement via a 2" galvanized pipe near the panel that was installed (probably for this purpose) when the house was built in the 1940s. The pipe is in a dry location. The run through the pipe is about six feet and total length of conduit would be about 10 feet plus whatever I add the basement for the final panel position. To make passing the wires easier, I plan to use separate conductors (three wires plus ground) rather than Romex.

    The first question is whether the concept is okay. Having a panel in the basement will allow me to wire 20 amp circuits for the kitchen and baths as well as install an electric dryer.

    Next is whether there are any height or other location requirements for the panel. The cast iron pipe enters the basement wall at about eight feet above the floor. A cast iron sewer pipe wraps around the basement wall at between five and six feet through the area where the conduit enters. So, where does the panel go? It seems like it would have to be either higher or lower than normal. Are there any code requirements about this?

    Thanks in advance and I’ll be back for more!
    dclynch's Avatar
    dclynch Posts: 202, Reputation: 19
    Full Member
     
    #2

    Jul 13, 2011, 09:17 AM
    Conduit materials
    Sorry if the first post was too involved.

    My question is whether I can use plumbing PVC (ie, white pipe) for the part of the conduit in my basement. The conduit in the garage from the main panel to the galvanized pipe is pretty straight and I'm using electrical PVC (gray pipe). I'd like the portion in the basement to make a fairly sharp turn to get to the subpanel. The plumbing parts are easier to get in my area and readily available in more shapes/sizes.

    I'm using 6 gauge THHN in the conduit protected by a 70 amp breaker.

    Thanks
    tkrussell's Avatar
    tkrussell Posts: 9,659, Reputation: 725
    Uber Member
     
    #3

    Jul 13, 2011, 01:59 PM
    I thought I answered the first post, it looks very familiar, I will need to check on that.

    As far as your second post, not, plumbing pipe cannot be used for electrical wiring, must be UL listed for electrical.

    And no, do not use plumbing fittings for elbows. Electrical fittings, such as LB, are available for hard 90 degree turns.
    dclynch's Avatar
    dclynch Posts: 202, Reputation: 19
    Full Member
     
    #4

    Jul 13, 2011, 02:07 PM
    Okay. It sounded good, but rules are rules.

    Thanks

Not your question? Ask your question View similar questions

 

Question Tools Search this Question
Search this Question:

Advanced Search

Add your answer here.


Check out some similar questions!

Basement subpanel [ 4 Answers ]

I want to install a 100 amp subpanel being fed from a 200 amp service panel,I intend to use #2 copper wire to feed this subpanel ,obviously I will have 3 , #2 copper and a green #4 for the ground . All wires will be in conduit and the subanel will be lass than 5ft. From the main service panel. I...

Installing a secondary subpanel. [ 11 Answers ]

I am installing a secondary subpanel in my basement/woodworking shop. The secondary break is 100 amp. There is no need for 240 volts and my equipment does not require it. I plan on only using one machine at a time but have several machines. The only item that will be running when a pwer tool is...

Installing a new subpanel [ 1 Answers ]

I have an existing 200-amp main panel with insufficient space to add the two 240-volt circuits needed for a dryer and range(these appliances are currently gas). I plan to install a 100-amp subpanel(main lug type) with neutral and ground isolated, adjacent to the main panel. I will have to relocate...

Installing a new subpanel [ 3 Answers ]

Hello, I am installing a subpanel in a utility shed and already have a panel in there using 2-60 amp tubes and another tube for the ground. What I would like to do is put a subpanel in there to where I can put four 20 amp breakers. The wire they ran already is a 10 gauge with 1 black 1 white and...

Installing a Subpanel [ 3 Answers ]

I'm setting up a woodshop in my garage and want to install a subpanel to run my equipment off (it's going to be right next to the main). I'm starting from scratch, knowing extremely little about how to accomplish this. What sort of box do I need to buy, how do I size the breaker that will feed...


View more questions Search